[Equest-users] District thermal energy
Brett Fero
bfero at robsonwoese.com
Tue Oct 5 13:29:25 PDT 2010
Neeraja,
Here are some answers;
Question 1: The third footnote below table G3.1.1A says to use the
predominant condition when more than 1 system can be applied.
Question 2: ASHRAE 90.1-2004 Exception G3.1.1a is the source of the 20,000
sf comment.
On Tue, Oct 5, 2010 at 10:01 AM, Neeraj Arora
<neeraj at kamalcogentenergy.com>wrote:
> Hi friends,
>
>
>
>
>
> I am working on a project which comes under "Required Treatment of District
> Thermal Energy in LEED-NC version 2.2 and LEED for Schools", Version 1.0,
> May 28, 2008 document.
>
>
>
> My project is a hotel building (80% residential and 20% non-residential).
> Hence as per my understanding the system type will be system 2 (residential,
> as per table G3.1.1A and G3.1.1B).
>
>
>
> I received a review comment which says that
>
>
>
> *Per ASHRAE 90.1-2004, tables G3.1.1A and G3.1.1B, the baseline system for
> this project shall be System #2 ? Packaged terminal heat pump. Also, since
> the project includes more than 20,000 square feet of non-residential space
> in addition to the large residential occupancy, all residential spaces
> should be modeled in the Baseline as System Type # 4 (if the total
> conditioned building area is less than 150,000 square feet) or System Type #
> 8 (if the total conditioned building area exceeds 150,000 square feet).
> Please include the requested information on the Template and revise the
> Tables 1.4, 1.8.1, 1.8.2 and the model as appropriate.***
>
>
>
>
>
> My questions are:
>
>
>
> 1. The project will come under residential category or non-residential
> category or both?? My system selection is correct??
> 2. Do anyone has the backup or support which confirms the line “*since
> the project includes more than 20,000 square feet of non-residential space
> in addition to the large residential occupancy,”?*
>
> * *
>
> Thanks in advance.
>
>
>
> Neeraj Arora
>
> Project Engineer
>
> Kamal Cogent Energy Pvt Ltd.
>
> 1st floor, Kamal Ratan Chambers,
>
> M.I.Road, Opp GPO
>
> Jaipur-302001, Rajasthan (India)
>
> Ph - 0091-141-2373184 / 85
>
> <http://neeraj@kamalcogentenergy.com>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
--
Brett Fero, P.E., CEM, LEED-AP
*RobsonWoese, Inc*
Salina Meadows Office Park
301 Plainfield Road, Suite 180
Syracuse, NY 13212
Ph: 315-445-2650
Fax: 315-445-0958
email: bfero at robsonwoese.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101005/1e6faa72/attachment.htm>
More information about the Equest-users
mailing list