[Equest-users] FW: Modeling inefficiencies of existing buildings

John Bixler JBixler at Sebesta.com
Tue Nov 30 13:43:51 PST 2010


I hadn't heard much back about the questions I raised below.  #3 in particular, I was hoping to rephrase and gain some additional insight:

In a existing building (system type, VAV reheat with very little turndown), where the airflows are known (and entered into equest), by adding duct leakage via the Duct Air Loss Ratio, with a low (near 0) Duct Air Loss OA (meaning very little of the leaked air "exfiltrates" the building), what would the expected result be?

Clearly the fans will operate more, so one would expect electric usage to increase.

But what would you expect the heating and cooling utilities to do?

From: John Bixler
Sent: Monday, November 08, 2010 7:37 PM
To: 'equest-users at lists.onebuilding.org'
Subject: Modeling inefficiencies of existing buildings

Hello all,

I've been using eQuest recently to support studies of existing buildings, and to evaluate the energy savings of different options.

I've struggled with trying to model some of the problems we've discovered in the older buildings.  Any thoughts on the following would be greatly appreciated.


1.       Failed reheat valves:  Reheat valves that are stuck in the open position.  Not only does this increase the heating hot water use, but it should affect fan energy and chilled water use as well.

2.       Light troffer diffusers:  All the vogue in the 60s and 70s, these combination lights and diffusers result in a large thermal gain as the air enters the zone.  eQuest has "duct delta T", however that assumes a heat loss under cooling.  This condition is always a gain of heat (and technically this will vary based on the temperature of the air entering the zone).

3.       Duct Leakage:  A massive problem until recently, measured leakage values can often be 30% or more.  eQuest has an apparent entry for this, however, each time I've enabled it, I've seen large REDUCTIONS in energy use.  Again, this is a condition that results in increased usage of all utilities as the zones struggle to meet their setpoints.



Also, duct leakage is assigned at the system level.  It appears eQuest then wants you to assign what plenum the duct is leaking "to".  Depending on how I specified my systems in the wizard, I have ended up with a plenum zone for each zone on a floor (which might mean 30 zones per floor) or one big plenum per floor.  If I have a system that serves zones on several floors, it dosent seem like eQuest will let me assign the leakage to go all the plenums the system is assigned to, evenly.  I have to pick a SINGLE zone that all the leakage goes to.



Thanks,

John Bixler, LEED AP BD+C
Mechanical Designer
Sebesta Blomberg
sebesta.com | P  319.364.1005 | M  319.558.9299

This message has been sent via the Internet. Internet communications are not secure against interception or modification. Sebesta Blomberg therefore can not guarantee that this message has not been modified in transit. This message and any files transmitted with it are confidential and intended solely for the use of the addressee. If you have received this message in error please notify the sender and destroy your copies of the message and any attached files.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101130/93280969/attachment.htm>


More information about the Equest-users mailing list