[Equest-users] Define a zone as open to below

Nick Caton ncaton at smithboucher.com
Tue Nov 23 07:06:21 PST 2010


I've played around with it in the past, and in my experience you will
not get accurate lighting behavior if you place the sensor remote from
the space whose lighting is being controlled.  It's not fresh in my
mind, but I believe if you look up the help entries regarding those
sensors you'll find eQuest handles them in a way that interacts directly
with its location in relation to the surfaces and fenestrations on the
interior of the space in question.

 

In short, if you wish to control lighting with daylight sensors in a
2-story space, it must be a single space/volume.  It sounds now like you
are trying to pull this off from the DD-wizards... I think your options
are more limited there.  You might try (1) adjusting the upper-level LPD
to account for the ground level lighting, or (2) making the multi-story
space a separate shell wrapped by the other(s)... the latter is
something I've done in the past but I'd recommend the detailed edit fix
I suggested below as a relative time/headache-saver.   

 

Further discussion between myself and others on this topic is in the
archives.

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

Smith & Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com 

 

From: Udana Ratnayake [mailto:udanasr at gmail.com] 
Sent: Monday, November 22, 2010 11:02 PM
To: Nick Caton
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Define a zone as open to below

 

I'm in need of placing a day light sensor to sense day light coming from
the skylights and control light level of the ground floor accordingly.
even though i make the first floor open to below the sensor doesn't seem
to take skylights in to account. is there anyway to sense the light
coming from skylights to control the lighting level with a sensor that
is placed in the floor below?

Thanx & Best Regards,
Udana.



On Sat, Nov 20, 2010 at 2:01 AM, Nick Caton <ncaton at smithboucher.com>
wrote:

Before I was aware of 'open to below' and similar options in the wizards
(oh, the perils of being self-taught!), I came up with a practice of
creating multi-story spaces by making separate zones for each level from
the wizard, then in detailed mode deleting all but the lowest, then
modifying the remaining space/zone to get the correct height/volume.

 

Some further tips:

-          Once done with the geometry edits, review that space's
internal loads - you may want to revise depending on your situation.  

-          You might consider for very tall spaces whether there is an
"unconditioned" layer from an HVAC perspective that you might want to
define as a separate, unconditioned space (think plenum).  

-          You can optionally pursue extra steps to tie the bounding
surfaces of adjacent spaces to the multi-story space if you deem it
necessary for accuracy.  If you anticipate you'll want to do this, pay
attention before deleting the individual multi-story spaces so that you
don't accidentally remove some surfaces you'd like to have associated
from the adjacent spaces... this is a case where thinking ahead a few
steps can save you a headache later.

 

~Nick

 

Error! Filename not specified.

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com
<http://www.smithboucher.com>  

 

From: equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] On Behalf Of Udana Ratnayake


Sent: Friday, November 19, 2010 1:03 AM
To: equest-users at lists.onebuilding.org

Subject: [Equest-users] Define a zone as open to below

 

I'm modeling a two storied building with a mezzanine area in the first
floor and i need to define the rest of the first floor area apart from
the mezzanine as open to below. is it possible to define a particular
zone as open to below in the detailed mode? if so how?
Thank you in advance. 

-- 
Udana




-- 
Udana

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101123/a79dbd25/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101123/a79dbd25/attachment.jpeg>


More information about the Equest-users mailing list