[Equest-users] Why Is There No Heating Capacity in PVAV Zones WhenConverted From PSZ in Detailed Edit?
James Hansen
JHANSEN at ghtltd.com
Wed Nov 10 10:54:57 PST 2010
Double check that your zone reheat entry has a value like 30 degrees, or
something around that value.
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA 22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com <http://www.ghtltd.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kathryn
Kerns
Sent: Wednesday, November 10, 2010 1:50 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Why Is There No Heating Capacity in PVAV Zones
WhenConverted From PSZ in Detailed Edit?
Everyone, I converted a model with a bunch of Pkgd Single Zone units
(furnace heat, DX cooling) to a Pkgd Var Vol system (electric heat, DX
cooling) with zones in Detailed Edit. The converted program ran but the
unmet heating hours increased greatly. I checked the new PVAVS zones,
and they are grouped correctly under the Pkgd Var Vol system, but the
program is not assigning any heating capacity to the individual zones. I
checked the heating capacities in the SV-A reports and all of the zone
capacities are 0. I then built a Design Wizard Pkgd Var Vol model and
started comparing the HVAC navigation tree screens to the Detailed Edit
converted model HVAC navigation tree screens and found some
discrepancies. I found that the converted Detailed Edit zones lacked the
minimum flow ratio (0.3) so I added that in. I also discovered that the
thermostat type didn't convert to Reverse Acting so I fixed that. I
don't see any other differences between the Design Wizard HVAC
navigation tree screens and the converted Detailed Edit HVAC navigation
tree screens, and yet the fact remains, I am not get any heating
capacity to show up in SV-A in the Detailed Edit converted model. So,
there is something else I need to change, but I can't think what.
Has anybody run across this problem before and has a solution?
Thanks.
Kathryn Kerns
Systems Specialist
BCE Engineers, Inc.
| Ph: 253.922.0446 | Fx: 253.922.0896 |
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101110/20094e04/attachment.htm>
More information about the Equest-users
mailing list