[Equest-users] Zoning Issue
    Brian Fountain 
    bfountain at greensim.com
       
    Wed Nov 10 07:44:22 PST 2010
    
    
  
You will have to define the common wall as an "adiabatic" interior 
partition -- no heat transfer and no solar load.  In the wizard you can 
do this by clicking on the wall (in Shell screen 2 of the DD wizard) and 
then selecting adiabatic.  In detailed mode you can also delete a 
exterior wall and then create an interior partition of type adiabatic.  
You could also simply delete the common wall -- this also has no solar 
and no conduction load.  The only thing this does is decreases the 
room's thermal mass slightly (not of significance likely).
There is no way to create and interior partition and to force the 
temperature of the adjacent space -- you would have to create the "next 
to" zone if you really want to model heat transfer between new and 
existing.  Unless the occupancies are significantly different, the 
impact of conduction across that wall is likely negligible.
Good luck.
BF
On 11/10/2010 10:36 AM, RJTHEACMAN at aol.com wrote:
> I am modeling an addition to an existing building. The new addition 
> has three perimeter exposures and the fourth exposure is up against 
> the existing building, which is a conditioned space.
>
> How do I tell equest that one of my exposures is not a perimeter wall 
> but it is basically a partition with a conditioned space adjacent to it?
>
> Thanks
>
> Richard J. Dominick, P.E.
> TEC Engineers LLC.
> The Energy Consultant
> 304 Main Avenue, Suite 426
> Norwalk, CT. 06851
> Phone: 203-722-5206
> Fax: 203-849-0781
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> No virus found in this message.
> Checked by AVG - www.avg.com <http://www.avg.com>
> Version: 10.0.1153 / Virus Database: 424/3248 - Release Date: 11/10/10
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101110/d23325e2/attachment.htm>
    
    
More information about the Equest-users
mailing list