[Equest-users] 100% Outdoor Air Systems
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Nov 4 11:05:48 PDT 2010
Jason,
The O/A flow rate IS equal to the supply flow rate, correct? So of
course you will want to model 240,000 CFM of O/A, to accurately model
the heating and cooling energy. I'm guessing you are really asking about
the exhaust. If you will be modeling heat recovery as an ECM, then the
exhaust flow rate and pathways are important. If not, you might get away
with modeling the exhaust rate identical to the supply flow. Either way,
I would try to figure out if the other 20% is being exhausted by other
fans, or exfiltrated or both. You could potentially zero out your
infiltration in some or all zones. Model the fan energy as best you can,
since it is likely to be high and a potential area for energy
improvement. You will probably need actual pressure measurements, rather
than design values, since the runaround loop (and associated pressure
drops) were removed.
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - the forest AND the trees. P
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jason
Moody
Sent: Thursday, November 04, 2010 1:42 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 100% Outdoor Air Systems
I have searched the archives and red all of the older opinions on this
topic but wanted to see if there are any new ideas on this topic. I
have a hospital that is served completely by 100% outdoor air units via
6 separate air handlers. Total supply cfm to the facility is 240,000
cfm. There are six large exhaust fans on the roof that remove
approximately 80% of that from the facility. Unfortunately there is no
heat recovery to date. They used to have a run around loop but it was
removed.
What is everyone's take on modeling this in equest? At first glance I
was planning on simply defining the amount of O/A to equal the supply
cfm but wanted some feedback before I continue.
Jason L. Moody, P.E.
RNM Engineers, Inc.
jmoody at rnm-engineers.com
828-456-9851
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101104/03e2d73f/attachment.htm>
More information about the Equest-users
mailing list