[Equest-users] Modeling below grade
Jeff Seger
Jeff.Seger at megroup.com
Tue Nov 2 12:38:36 PDT 2010
You need to model basement as a separate shell from the other 4 floors. You then need to change "Exposure" on wizard screen 3/25 for the above grade floors to "Over Conditioned Space (adiabatic)".
That should be all you need.
Jeff Seger, EIT
M.E. GROUP / design + green
t: 816.531.2121 x3123
[cid:image001.jpg at 01CB7A9B.A1B7FBE0]<http://www.megroup.com/>
From: aida darghouth asli [mailto:darghouthasli.aida at gmail.com]
Sent: Tuesday, November 02, 2010 7:06 AM
To: Equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling below grade
Dear all,
I am trying to model a building with 4 floors and 2 basements with eQUEST. I succeffuly imported the .dwg file and modeled the above grade part but i have aproblem with the below grade since it doesnt have the same shape as the ground floor.
Please provide me with your advice as soon as possible.
Thank you
DAKA
________________________________
CONFIDENTIALITY NOTICE: This e-mail and any attached file(s) are intended only for the use of the individual or entity to whom or to which it is addressed and may contain information that is privileged, confidential, proprietary, and trade secret. If the reader of this message is not the intended recipient or an employee or agent responsible for delivering the message to the intended recipient, you are hereby notified that any dissemination, distribution, or reproduction of this communication is strictly prohibited. If you have received this communication in error, please notify us immediately and discard the original message and any attachment(s).
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101102/77925aeb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 11807 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20101102/77925aeb/attachment.jpg>
More information about the Equest-users
mailing list