Scott,
Be aware that the eQUEST input fields that say "MBtu/h" are millions,
not thousands, of Btu/h. So a typical boiler capacity might be entered
as 1.0, not 1,000.
Regards,
Bill
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P May is National Bike Month. Bike to Work Day May 21st.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Tomlinson, Scott
Sent: Friday, May 28, 2010 8:53 AM
To: Daniel Deese; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest Users - hydronic question
Daniel,
Thanks for the reply. My input ratios are right. If I allow autosizing
my results are reasonable. The only thing I change is adding capacities
and my results just go nuts.
- Scott
From: Daniel Deese [mailto:Daniel.Deese at crbusa.com]
Sent: Thursday, May 27, 2010 3:57 PM
To: Tomlinson, Scott; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] eQuest Users - hydronic question
Scott,
Be sure to check your Heat Input Ratios (HIR) and your
Electric Input Ratios (EIR). For a chiller, if your COP is 5.0, your
EIR would be 0.2. For a boiler, if your efficiency is 80%, then your
HIR is 1.25. If I'm wrong, someone correct me, but I had a huge heat
rejection load one time only to find out that my EIR for the chiller was
1.2, instead of 0.2. thanks.
daniel
Daniel I. Deese, EI| CRB Consulting Engineers |
1255 Crescent Green, Suite 350 | Cary, NC 27518 |
P: 919-852-5443 | F: 919-852-5454 | X: 4543
Email: daniel.deese at crbusa.com <mailto:daniel.deese at crbusa.com>
________________________________________________________________________
________________
This document may contain confidential information and is intended for
use by the addressee only. If you are not
the intended recipient, please do not transmit, copy, disclose, or
utilize this communication in any manner. If you
received this message in error, please notify the sender immediately and
delete this message.
* Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Tomlinson, Scott
Sent: Thursday, May 27, 2010 1:05 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest Users - hydronic question
Dear eQuesters,
Whenever I try to add equipment capacities to anything hydronic, be it a
boiler, chiller, or anything else, my energy consumption goes absolutely
crazy. Is anyone else experiencing this?
- Thank you,
__________________________________________
Scott Tomlinson, PE, LEED-AP
Mechanical
Symmes Maini & McKee Associates, Inc.
1000 Massachusetts Avenue, Cambridge, MA 02138
t: 617.520.9438
f: 617.354.5758
stomlinson at smma.com
www.smma.com <http://www.smma.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100528/1c3bf2a6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 14792 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100528/1c3bf2a6/attachment.jpeg>
More information about the Equest-users
mailing list