[Equest-users] Building Orientation Accuracy?
Nick Caton
ncaton at smithboucher.com
Mon May 17 13:24:45 PDT 2010
Otto,
I just looked at your revised files - you are still modeling two
seemingly fairly different classrooms. Note your "North" classroom has
adiabatic internal walls/ceiling and your "South" classroom has heat
transferring ones. I haven't scoured for other differences that may
well be in there regarding schedule assignments and such - I don't know
of a fast way to do so.
If you're truly concerned with eQuest's ability to correctly account for
a varying azimuth and want to test it, you could make your task easier
by creating a square classroom with identical walls on each side and
observe identical results with 0,90,180,270 degree azimuths.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Monday, May 17, 2010 3:07 PM
To: Paul Riemer; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Building Orientation Accuracy?
I fixed the differences and now I get the following results:
North Facing: Space Cooling: 4.1 MBTU, Space Heating: 21.7 MBTU
South Facing: Space Cooling: 4.3 MBTU, Space Heating: 18.7 MBTU
When I change the orientation 180 degrees, the results are:
North Facing: Space Cooling: 3.8 MBTU, Space Heating: 22.6 MBTU
South Facing: Space Cooling: 3.6 MBTU, Space Heating: 17.8 MBTU
These also seem incorrect for the same reason.
From: Paul Riemer [mailto:Paul.Riemer at dunhameng.com]
Sent: Monday, May 17, 2010 3:56 PM
To: Otto Schwieterman; equest-users at lists.onebuilding.org
Subject: RE: Building Orientation Accuracy?
Otto,
Your north and south have different inputs. I specifically noted
plenums temperature set points and plenum floor weight.
I suggest you clean it up and run it again.
Paul Riemer
Dunham
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Monday, May 17, 2010 2:39 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Building Orientation Accuracy?
I have noticed that eQUEST does not accurately determine the cooling and
heating loads when rotating the building 180 degrees using the Azimuth
feature under the building properties in the detailed edit mode. I
created and attached a file where there are two classrooms. One
classroom faces north and one faces south.
When I run the simulation I get the following results:
North Facing: Space Cooling: 4.1 MBTU, Space Heating: 21.9 MBTU
South Facing: Space Cooling: 4.3 MBTU, Space Heating: 18.9 MBTU
When I change the orientation 180 degrees, the results are:
North Facing: Space Cooling: 3.9 MBTU, Space Heating: 23.0 MBTU
South Facing: Space Cooling: 3.6 MBTU, Space Heating: 18.1 MBTU
When I rotate the site 180 degrees the north and south facing energy
consumption is different (they should be exactly the same). Also, the
space cooling does not make sense because the building's weather file is
Dayton Ohio and the south facing classroom should use more cooling than
the north facing classroom.
This makes me assume that eQUEST has a problem with building rotation in
the detailed edit mode.
Please check to see if I am assuming this correctly because this will
affect every LEED project.
Otto Schwieterman
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity. If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance.
________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity. If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail. Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful. Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/cb8cfb28/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/cb8cfb28/attachment.jpeg>
More information about the Equest-users
mailing list