[Equest-users] Building Orientation Accuracy?

Otto Schwieterman oschwieterman at fhai.com
Mon May 17 13:06:39 PDT 2010


I fixed the differences and now I get the following results:

 

North Facing: Space Cooling: 4.1 MBTU, Space Heating: 21.7 MBTU

South Facing: Space Cooling: 4.3 MBTU, Space Heating: 18.7 MBTU

 

When I change the orientation 180 degrees, the results are:

North Facing: Space Cooling: 3.8 MBTU, Space Heating: 22.6 MBTU

South Facing: Space Cooling: 3.6 MBTU, Space Heating: 17.8 MBTU

These also seem incorrect for the same reason.

 

From: Paul Riemer [mailto:Paul.Riemer at dunhameng.com] 
Sent: Monday, May 17, 2010 3:56 PM
To: Otto Schwieterman; equest-users at lists.onebuilding.org
Subject: RE: Building Orientation Accuracy?

 

Otto,

Your north and south have different inputs.  I specifically noted
plenums temperature set points and plenum floor weight.

I suggest you clean it up and run it again.

Paul Riemer

Dunham

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Otto
Schwieterman
Sent: Monday, May 17, 2010 2:39 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Building Orientation Accuracy?

 

I have noticed that eQUEST does not accurately determine the cooling and
heating loads when rotating the building 180 degrees using the Azimuth
feature under the building properties in the detailed edit mode. I
created and attached a file where there are two classrooms. One
classroom faces north and one faces south. 

 

When I run the simulation I get the following results: 

 

North Facing: Space Cooling: 4.1 MBTU, Space Heating: 21.9 MBTU

South Facing: Space Cooling: 4.3 MBTU, Space Heating: 18.9 MBTU

 

When I change the orientation 180 degrees, the results are:

 

North Facing: Space Cooling: 3.9 MBTU, Space Heating: 23.0 MBTU

South Facing: Space Cooling: 3.6 MBTU, Space Heating: 18.1 MBTU

 

When I rotate the site 180 degrees the north and south facing energy
consumption is different (they should be exactly the same). Also, the
space cooling does not make sense because the building's weather file is
Dayton Ohio and the south facing classroom should use more cooling than
the north facing classroom.

 

This makes me assume that eQUEST has a problem with building rotation in
the detailed edit mode. 

 

Please check to see if I am assuming this correctly because this will
affect every LEED project.

 

Otto Schwieterman

 

 

________________________________________________________________________
________________
Fanning/Howey Associates, Inc. intends to send this transmission
(including any attachments) only to the
designated individual or entity.   If you received this message in
error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number
indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to
ensure no viruses are present in the
electronic mail.  Fanning/Howey Associates, Inc., will not accept
responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure,
dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe
unlawful.   Any information included in
this transmission that is not related to contracts with our
authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability
insurance. 
 

________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity.   If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail.  Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful.   Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/2e38eb02/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: South Baseline 2.inp
Type: application/octet-stream
Size: 59744 bytes
Desc: South Baseline 2.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/2e38eb02/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: South Baseline 2.pd2
Type: application/octet-stream
Size: 13944 bytes
Desc: South Baseline 2.pd2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/2e38eb02/attachment-0001.obj>


More information about the Equest-users mailing list