[Equest-users] Cooling Energy and Exhaust air heat recovery

Bassam Yammine byammine at flowgroup.ca
Mon May 17 10:05:24 PDT 2010


Hi Ahmed, not knowing the details of your system and model, but in
general by having an ERV, your system may not be able to take advantage
of the free cooling when outdoor air temperatures are below your return
air temperature and there is cooling demand. It seems from your numbers
that free cooling could be available for many days during the year.
During the cooling season, and unless it is bypassed, your ERV may  be
preheating cool before it enters the space.

 

Regards,

Bassam

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ahmed
Azhari
Sent: Monday, May 17, 2010 8:21 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Cooling Energy and Exhaust air heat recovery

 

Hello Users, 

 

I have a packaged (Heating: Gas-Fired, Cooling: DX) air handling unit
with VAV boxes in the zones. The cooling coil control for the AHU is
Zone reset. I have noticed an odd behavior in the cooling side when I
model an exhaust air heat recovery as follow:

 

    

The cooling energy increase from 67.7MBTU to 132MBTU when I include 70%
exhaust air heat recovery which doesn't physically make sense to me.

 

When I change the cooling coil control to Outdoor air reset the results
change as follow:

 

 

 

The above scenario makes sense in a way that both the heating and
cooling energy decreased by incorporating exhaust air heat recovery.  

 

I appreciate any explanation on the strange behavior of scenario I

 

Best Regards, 

________________________________________________________________________
__

Ahmed Azhari, B.Eng., LEED(r) AP

Energy Analyst

 

Jain Sustainability Consultants Inc.

 

2260 Argentia Road, 2nd Floor

Mississauga, Ontario L5N 6H7, CANADA

Tel:  (905) 542 7211 Ext 234

Fax: (905) 542 7622

Email: aazhari at jainconsultants.com <mailto:aazhari at jainconsultants.com> 

Web: www.jainassoc.com <http://www.jainassoc.com/> 

 

NOTICE OF CONFIDENTIALITY
This communication, including any attachments, is intended only for the
use of the addressees and is confidential. 

If you received this communication in error, please permanently delete
the entire communication from any computer or other storage medium.

 

 Please consider your environmental responsibility before printing this
e-mail & any documents

 



__________ Information from ESET Smart Security, version of virus
signature database 5121 (20100517) __________

The message was checked by ESET Smart Security.

http://www.eset.com

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/5c28e583/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 15254 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/5c28e583/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 14224 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/5c28e583/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 1257 bytes
Desc: image004.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100517/5c28e583/attachment.gif>


More information about the Equest-users mailing list