[Equest-users] Daylight Schedules/Controls
Nick Caton
ncaton at smithboucher.com
Fri May 14 14:51:43 PDT 2010
Omar,
I think (and I'm encouraging you to confirm - this is just from memory)
if you explore the help files you'll find that daylighting controls
crank out an hourly fractional multiplier to apply to the space lighting
kW. If you have a fractional lighting schedule (instead of ON/OFF),
then that hourly fraction would be applied as well - useful if you want
to simultaneously explore blanket reductions or account for occupancy
sensors in the way 90.1 would have us do it.
Example: If you have 10kw of lighting in a space, a fractional lighting
schedule of 0.9 and your daylighting controls dim your fixtures' input
watts to 0.2 of full for a given hour, then your hourly consumption
would be 0.9x0.2x10kW = 1.8kW. 1.8kW would apply for electrical
consumption and would be passed on to the thermal loads portion of the
program, where it might be reduced/modified by sensible and/or latent
fractions and/or the various "fraction to space/plenum" inputs you may
decide to define, to determine the hourly internal heat contribution.
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar
Katanani
Sent: Friday, May 14, 2010 3:56 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Daylight Schedules/Controls
Dear all,
I am editing my building using the detailed design mode. I want to set
the lighting control for each zone. I double click on each zone, then go
to lighting and set it (on/off, dimming...etc).
However, I noticed that I can set lighting schedules also. Won't this
contradict with the lighting strategy? What shall I do with the lighting
schedules then?
Your help is greatly appreciated!
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Chawkatly Building (Valli & Valli), 6th floor
Charles Helou Street, Saifi District
Beirut, Lebanon
Mobile: +961 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0)207 939 0989
Fax: +44 (0)207 939 0981
Website: www.ecoconsulting.net
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100514/428d5d8c/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100514/428d5d8c/attachment.jpeg>
More information about the Equest-users
mailing list