[Equest-users] VRV systems

Otto Schwieterman oschwieterman at fhai.com
Thu May 13 08:14:52 PDT 2010


I would open a new project in the wizard and create an air to air heat
pump system. I would input the performance values for heating and
cooling, then I would go to the detailed edit mode and use the heating
and cooling performance values that eQUEST calculated (generally, EER
and COP performance ratings include fan energy, when you input the
ratings into the wizard, eQUEST breaks out the fan energy and gives you
a new performance rating) and use those values for your model.

 

You would want to choose the type of compressor that the VRV/VRF system
is designed for/actually is.

 

From: sambhav tiwari [mailto:tiwari.sambhav at gmail.com] 
Sent: Thursday, May 13, 2010 6:27 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] VRV systems

 

Dear Otto Schwieterman,
                                          I am using Visual DOE 4.1 for
energy simulation and i have followed the techinque told by you for
modelling VRV systems . I created a Air to Air heat pump in my heating
tab .But when i created it ,it is asking the COP of the heat pump should
i  enter the VRV COP in the heat pump COP?? in heating tab , or in my
cooling tab it is also  asking for DX system COP?  where should i enter
my VRV system COP?
 

Also the option to make compressor as one two or variable speed is
comming in my air to air heat pump is it ok.


I look forward for your valuable response.

Thanks
Sambhav Tiwari.


________________________________________________________________________________________
Fanning/Howey Associates, Inc. intends to send this transmission (including any attachments) only to the
designated individual or entity.   If you received this message in error, please notify the sender by replying
to the electronic mail (if electronic) or by telephone at the number indicated on this document.
Fanning/Howey Associates, Inc. has taken reasonable precautions to ensure no viruses are present in the
electronic mail.  Fanning/Howey Associates, Inc., will not accept responsibility for any loss or damage arising
from the use of this electronic mail or attachments. Use, disclosure, dissemination, distribution, or reproduction
of this message by unintended recipients is not authorized and maybe unlawful.   Any information included in
this transmission that is not related to contracts with our authorization, verbal or written, by Fanning/Howey
Associates, Inc. may not be covered by our professional liability insurance. 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100513/9cdc77b2/attachment.htm>


More information about the Equest-users mailing list