[Equest-users] Error Message

Lauren Rosenthal Lauren.Rosenthal at arup.com
Mon May 10 11:32:10 PDT 2010


Thanks so much, increasing the SAT worked perfectly.

____________________________________
Lauren Rosenthal
Mechanical Engineer
 
Los Angeles CA

-----Original Message-----
From: B. Fountain [mailto:bfountain at greensim.com] 
Sent: Monday, May 10, 2010 11:23 AM
To: Lauren Rosenthal
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Error Message

The 1st warning message is because you have a maximum humidity setpoint
set so the discharge air temperature is being set down to deliver
dehumidification.

The 2nd error message is because the coil leaving air temperature (which
is the cool set T less the temperature pick up across the fan)is not more
than 6F above your chilled water return water temperature.  Solutions:
increase your minimum supply air temperature, decrease the fan pick-up
temperature, select the fan as blowthrough or select motor out of the
airstream.



> Hello all,
>
>
>
> I've received this error message several times and can't figure out
> which input needs to be revised - any help would be great.
>
>
>
> **WARNING***************************************************************
> *******
>
>              In AHU-0-27_ConsSprayRmMUA (MASTER), the return humidity
> for a coil exit T of  47.4 is 0.0065
>
>              Your setpoint is 0.0005, which may not be held.
>
>
>
>
> ***ERROR****************************************************************
> *******
>
>              In AHU-0-27_ConsSprayRmMUA (MASTER), cooling coil leaving
> temperature must
>
>              be at least 6F higher than entering water temp.
>
>
>
>
>
> ____________________________________
>
> Lauren Rosenthal
>
> Mechanical Engineer
>
>
>
> Los Angeles CA
>
>
>
> ____________________________________________________________
> Electronic mail messages entering and leaving Arup  business
> systems are scanned for acceptability of content and viruses
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>





More information about the Equest-users mailing list