[Equest-users] how to turn off heat/scheduling

Paul Brooks equestpaul at yahoo.com
Fri May 7 13:20:34 PDT 2010


for my base LEED model I am using electric re-heat at VAV boxes.  I have the issue there.  I think I just have to turn it off to make all of this work.....i think.




________________________________
From: "Walson, Kristy" <kristy.walson at tlc-eng.com>
To: Paul Brooks <equestpaul at yahoo.com>; eQuest user forum <equest-users at lists.onebuilding.org>
Sent: Fri, May 7, 2010 4:18:24 PM
Subject: RE: [Equest-users] how to turn off heat/scheduling


Hi Paul,
 
Click through all the tabs in the Heating inputs and make sure you don't have any supplementary heat in there that shouldn't be included.  I believe eQuest add a supplementary furnace automatically to all systems and you have to remove it.  I hope this helps.
 
Kristy Walson, PE, LEED AP
Mechanical Engineer / Sustainable Design
 
From:equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Brooks
Sent: Friday, May 07, 2010 4:14 PM
To: eQuest user forum
Subject: [Equest-users] how to turn off heat/scheduling
 
I am getting a heat load in the middle of the cooling season.  I don't believe it.  the system is VAV, chilled water with reheat coils at the boxes only.  Office Building in a semi-tropical zone (3). 
 
I understand that I should be able to turn the heat off/make unavailable, but the instructions on how seem cryptic.....that or my brain is overloaded.  Can someone provide a quick answer ton how to do it?
 
Thanks!


      