[Equest-users] eQUEST: Hours outside throttling range for Standard VAV w/Reheat

John Aulbach jra_sac at yahoo.com
Thu May 6 09:32:20 PDT 2010


Gordon:

Try increasing the throttling range to 6 DegF. Also find out WHEN your unmet hours exist by looking at SS-O reports, which show 8760 of space temperatures based on time of day.  If I get a chance later today, I will look at your run.

John R. Aulbach, PE, CEM
Senior Energy Engineer

________________________________

PartnerEnergy
1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745
www.ptrenergy.com| jaulbach at ptrenergy.com




________________________________
From: Gordon D. Schweitzer <GDSchweitzer at heapy.com>
To: equest-users at lists.onebuilding.org
Sent: Thu, May 6, 2010 6:31:57 AM
Subject: [Equest-users] eQUEST: Hours outside throttling range for Standard VAV w/Reheat


All,
 
I am modeling a "Standard VAV w/Reheat" for a small college building (~20,000 SF) and am having some difficulty reducing my hours outside of throttling range. I have tried increasing my "Throttling Range" to 4 F, increasing my system size capacity (from 1.15 to 2), and have also adjusted my "Heat Temp Schedule" to turn all but one zone to default to create a 'control zone' for the system.  However, I still have many unmet hours (~39% of hours outside of throttling range - my BEPU report does not identify hours, but rather a % (reference previous Equest thread)).
 
Any suggestions are certainly welcome!
 
Thanks in advance,
 
Gordon


      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100506/a183eae2/attachment.htm>


More information about the Equest-users mailing list