[Equest-users] eQUEST: Hours outside throttling range for Standard VAV w/Reheat

Pasha Korber-Gonzalez pasha.pkconsulting at gmail.com
Thu May 6 08:58:04 PDT 2010


Gordon, go to the SS-F reports for each zone in your DOE2 output, here you
will be able to identify which zones suffer from underconditioning and
whether it is heating or cooling energy that is insufficient.  If it is
heating energy (i.e. underheated) which is my guess for your model then you
can adjust items to offer more heating energy.  You might want to install
baseboards in your system & zones, you may need to adjust your reheat coil
delta T, or something else.

You can always send us your .pd2 & .inp files so that we can open up your
project, review it and give you some suggestions.

pasha

On Thu, May 6, 2010 at 7:31 AM, Gordon D. Schweitzer <GDSchweitzer at heapy.com
> wrote:

>  All,
>
> I am modeling a "Standard VAV w/Reheat" for a small college building
> (~20,000 SF) and am having some difficulty reducing my hours outside of
> throttling range. I have tried increasing my "Throttling Range" to 4 F,
> increasing my system size capacity (from 1.15 to 2), and have also adjusted
> my "Heat Temp Schedule" to turn all but one zone to default to create a
> 'control zone' for the system.  However, I still have many unmet hours (~39%
> of hours outside of throttling range - my BEPU report does not identify
> hours, but rather a % (reference previous Equest thread)).
>
>  Any suggestions are certainly welcome!
>
> Thanks in advance,
>
> Gordon
>
>   <http://www.heapy.com/>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100506/e8f926c3/attachment.htm>


More information about the Equest-users mailing list