[Equest-users] Frame Data in eQUEST from a WINDOW5 file
Alex Krickx
akrickx at seriousmaterials.com
Wed May 5 17:01:53 PDT 2010
Thanks Cassie,
I just got an email from someone at LBL saying the same thing. Since this is the case, do people see a big benefit of importing the WINDOW5 files rather than manually entering the COG U-factors and SC? It seems that since no one file can be used for parametric window analysis (glass and frame) is it still useful to have the COG WINDOW5 file? I could imagine that for a daylighting analysis it's important to know all of the specific glazing properties, but is the same true thermal/energy analysis using eQUEST?
Cheers,
Alex
From: Cassie Waddell [mailto:Cassie.Waddell at arup.com]
Sent: Wednesday, May 05, 2010 4:56 PM
To: Alex Krickx; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Frame Data in eQUEST from a WINDOW5 file
Alex,
The window import within eQuest does not include the frame effects. This needs to be specified directly within the model. It's a bit misleading because you can only generate the report from within the window tab (compared to the glazing system tab). Hopefully this will change in future versions of either eQuest or Window...
Cassie
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Alex Krickx
Sent: Wednesday, May 05, 2010 4:28 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Frame Data in eQUEST from a WINDOW5 file
Hello all,
First and foremost, happy Cinco de Mayo! I have a question about how eQUEST imports WINDOW5 files and I am hoping the group can provide some guidance:
Is there a way for eQUEST to import the frame data from a WINDOW5 report, or does the user need to separately change the frame conductance?
I imported two WINDOW5 files (same glass, different frame conductance) into eQUEST fine and set up a parametric run (component type: window; category: basic specs; keyword: glass type; Value: 'imported W5 file'). The problem is that the resulting energy consumption was the same.
I've attached the two WINDOW5 files and a very simplified eQUEST model that shows how I set up my parametric runs. Regarding the W5 files: on line 9 it gives the frame conductance in metric units.
Thanks in advance for your help!
Kind regards,
Alex Krickx
Alex Krickx
Building Energy Specialist
[cid:image001.jpg at 01CAEC74.A94763B0]
1250 Elko Dr, Sunnyvale, CA 94089
(t) 408.541.8124
Warning: The information contained in this e-mail may be privileged attorney-client communications or attorney work product and/or proprietary and confidential. If the reader of this message is not the intended recipient then you have received it in error and any review, distribution or copying of this message is prohibited and you are to notify us immediately by reply e-mail and delete the original message immediately.
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100505/f20d5008/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5602 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100505/f20d5008/attachment.jpg>
More information about the Equest-users
mailing list