[Equest-users] Minimum Efficiency System 5
Jason Glazer
jglazer at gard.com
Wed May 5 06:52:14 PDT 2010
The test procedure differentiates the equipment. If it is
rated using ARI 390 then it is a SPVAC while different ARI
test procedures are used for Table 6.8.1A equipment. I have
always believed that System 5 "packaged rooftop VAV with
reheat" from Table G3.1.1B is referencing Table 6.8.1A
single packaged equipment.
Jason
On 5/4/2010 6:48 PM, Carol Gardner wrote:
> 90.1P ECB Subcommittee can you provide us with some definition? Mike R?
> Jason? Help!
>
>
> On Tue, May 4, 2010 at 12:47 PM, Bishop, Bill <wbishop at pathfinder-ea.com
> <mailto:wbishop at pathfinder-ea.com>> wrote:
>
> So what’s the difference (other than minimum efficiency) between a
> 230,000 Btu/h single package air conditioner in Table 6.8.1A and a
> 230,000 Btu/h single package vertical air conditioner in Table 6.8.1D?
>
> I guess the SPVAC is installed on an outside wall (per the
> definition in Section 3.2), but I don’t see where units in Table
> 6.8.1A are necessarily rooftop units per the Table G3.1.1B requirement.
>
> *William Bishop, EIT, BEMP, LEED^® AP **|** **Pathfinder Engineers &
> Architects LLP***
>
> Mechanical Engineer
>
> 134 South Fitzhugh Street
> Rochester, NY 14608
> T: (585) 325-6004 Ext. 114
> F: (585) 325-6005
>
> wbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>
>
> www.pathfinder-ea.com <http://www.pathfinder-ea.com>
>
> P Please strive to live sustainably.
>
> ------------------------------------------------------------------------
>
> *From:* equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
> *Demba Ndiaye
> *Sent:* Tuesday, May 04, 2010 3:07 PM
> *To:* Pasha Korber-Gonzalez; Cam Fitzgerald
>
> *Cc:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] Minimum Efficiency System 5
>
> You indeed have to use Table 6.8.1A. The units in Table D are for
> the terminal units (they are normally un-ducted, in direct contact
> with the space they serve).
>
> _____________
>
> Demba NDIAYE
>
> *From:* equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
> *Pasha Korber-Gonzalez
> *Sent:* Tuesday, May 04, 2010 1:58 PM
> *To:* Cam Fitzgerald
> *Cc:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] Minimum Efficiency System 5
>
> Cam,
>
> I'm curious to where you found the reference for a "single package"
> sub-category and how it is pointing to table A to be used for
> performance factors of packaged equipment as opposed to table D
> which is specific to packaged a/c units.
>
> I looked back through 90.1 and can't find any notes or guidance to
> follow your recommendation to point me to table 6.8.1A. Can you
> please provide more specific reference to where you are getting this
> info from Appendix G? This could be a significant thing for the
> rest of us to learn and for me to correct if I have missed the info
> you are refering to.
>
> Thanks for your help on this.
>
> pasha
>
> On Tue, May 4, 2010 at 6:30 AM, Cam Fitzgerald
> <cam at energyopportunities.com <mailto:cam at energyopportunities.com>>
> wrote:
>
> Omer:
>
> For system type 5 you should be using sub-category “single package”
> with the appropriate heating section type from Table 6.8.1A. Table
> 6.8.1D applies to system types 1 and 2, small packaged terminal units.
>
> Hope this helps. Have a great day!
>
> Cam S. Fitzgerald, PE, LEED AP
>
> Energy Opportunities, LLC
>
> a 7group company
>
> e-mail: fitzgerald at sevengroup.com <mailto:fitzgerald at sevengroup.com>
>
> *From:* equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>
> [mailto:equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
> *Pasha Korber-Gonzalez
> *Sent:* Tuesday, May 04, 2010 5:30 AM
> *To:* Ömer Moltay
> *Cc:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
>
>
> *Subject:* Re: [Equest-users] Minimum Efficiency System 5
>
> Omer,
>
> I would use 6.8.1D. Just because you are looking at a COP value
> doesn't mean that it wasn't originally an EER or SEER value, you
> might want to back out the EER value from your equivalent COP and
> see if you can reference it from the 6.8.1D table for Packaged
> equipment performance.
>
> pasha
>
> 2010/5/4 Ömer Moltay <omoltay at mimtarch.com
> <mailto:omoltay at mimtarch.com>>
>
> Dear All,
>
> What would you choose as the minimum efficiency for baseline
> modelling for the DX cooling (923 kW) of System Type 5 from Appendix
> G (Packaged rooftop VAV with reheat)? I am looking at a model
> previously done by someone else and the COP has been chose as 2.96,
> which could mean that they have used Table 6.8.1A - Condensing
> units, air cooled. But I am not sure if this should be correct.
>
> Thanks,
>
> Ömer Moltay, LEED AP
> Mimta Ltd.
> Hekimsuyu Cad. 559. Sk. No:39
> 34255 Kucukkoy Istanbul Turkey
> Tel: 90-212-617-2296
> Fax: 90-212-617-2297
> www.mimtarch.com <http://www.mimtarch.com/>
>
> Sürdürülebilir Binalar Blog
> http://surdurulebilirbina.blogspot.com
> <http://surdurulebilirbina.blogspot.com/>
>
> Green Building in Turkey on LinkedIn
> http://www.linkedin.com/groups?gid=2278249
>
> ----- Original Message -----
>
> *From:* Piyush Varma <mailto:varpiyush at gmail.com>
>
> *To:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
>
> *Sent:* Tuesday, May 04, 2010 11:55 AM
>
> *Subject:* [Equest-users] Queries
>
> Hi all,
>
> I am an eQuest newbie and had 2 small queries which hopefully
> would be answered.
>
> 01. What's the logic behind eQuest giving positive (+ve) Cooling
> Loads & (-ve) negative Heating Loads. (I made an Admittance
> Method Algorithm & it gives me the opposite values, eQuest i.e.
> negative cooling loads & +ve heating loads, have checked all
> sign convention...can't figure out why? My algorithm simulates
> for Delhi's (India) climate predominantly, cooling loads.
>
> 02. I have asked this before...is there any library for data of
> alternating solar gain factors, especially for Delhi, India. (As
> far as i believe it does'nt take into account the alternating
> solar gain factor...)
>
> hope these get resolved soon, thanks in advance.
>
> Regards,
>
> Piyush
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Jason Glazer, P.E., GARD Analytics, 90.1 ECB chair
Admin for onebuilding.org building performance mailing lists
More information about the Equest-users
mailing list