John, 

 

If you edited your project in detailed mode, you will not be able to
recreate the inputs with pd2 file alone. If your main 'MyProject.inp' file
is corrupted, I'd check in the project folder to see if you have other
usable inp files such as 'MyProject -Baseline Design.inp' or ''My Project -
1.inp' (created by Parametric Run tool). You can pick the workable inp file
for the run that is most similar to your main project (contains fewer
parametric changes), save it as 'MyProject.inp', open the project in eQUEST
main interface, and update the inputs that were different in the surrogate
inp file. For example if you used inp file for the parametric run that
changed building azimuth (App G baseline rotations), you would change the
azimuth back to reflect the actual orientation. 

 

Good luck, 

 

Maria 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Aulbach
Sent: Tuesday, May 04, 2010 2:20 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] The mysterious disappearing .INP file..

 

This happened to me before, but I do not remember how to recreate the.INP
file. I have the complete (I think) .PD2 files, so I think this should be
able to recreate the .INP file. There IS still an .INP file, but has
virtually nothing in it.

 

Any suggestions?

 

 

John R. Aulbach, PE, CEM

Senior Energy Engineer

  _____  

Partner Energy

1990 E. Grand Avenue, El Segundo, CA 90245
W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745

 <http://www.ptrenergy.com/> www.ptrenergy.com
<mailto:%7C%20jaulbach at ptrenergy.com> | jaulbach at ptrenergy.com

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100504/8c9eb077/attachment.htm>


More information about the Equest-users mailing list