[Equest-users] Process Equipment Power Consumption
Gaurav Mehta
gmehta75 at gmail.com
Mon May 3 21:20:15 PDT 2010
Please refer to the Chapter 18, Nonresidential Cooling and Heating Load
Calculations of the 2009 ASHRAE Handbook of Fundamentals.
Best regards,
Gaurav Mehta
Stantec
--------------------------------------------------
From: "Walson, Kristy" <kristy.walson at tlc-eng.com>
Sent: Monday, May 03, 2010 11:29
To: <omoltay at mimtarch.com>; <equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Process Equipment Power Consumption
> Hi Omer,
>
> On recent projects, I have had to pay more attention to the process loads
> for the types of equipment you mentioned below. In the past, I would just
> ensure that my process energy cost was 25% of the total energy cost
> because I knew that the types of buildings I was modeling (commercial
> offices, mostly) would never have an actual process load even close to
> 25%.
>
> However, recently I have been modeling process loads in a more exact way.
> What I do is I take the kW rating of the equipment, then I talk to the
> electrical engineer to get an idea of whether that equipment will ever run
> at its rated load and, if not, I apply the appropriate reduction to it
> based on what the electrical engineer says.
>
> Once I have this maximum energy use for process loads in the building, I
> then create a custom schedule for this process energy. Sometimes I need
> to create more than one custom schedule based on the type of equipment in
> the space. This can become very tedious if you get too far into the
> weeds, so I try to keep the schedules realistic, but simple and I keep the
> number of different custom schedules I create to a minimum. As we all
> know, you can never know the actual occupancy and use schedule of a
> building until it is occupied for a certain period of time, so keep your
> assumptions simple and logical.
>
> I'd love to hear what other folks are doing if it differs from my process.
>
> Kristy Walson, PE, LEED AP
> Mechanical Engineer / Sustainable Design
>
> -----Original Message-----
> From: equest-users-bounces at lists.onebuilding.org
> [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
> omoltay at mimtarch.com
> Sent: Monday, May 03, 2010 1:46 PM
> To: equest-users at lists.onebuilding.org
> Subject: [Equest-users] Process Equipment Power Consumption
>
> Dear All,
>
> One of the things that cause most trouble for us in modelling is the power
> consumption of equipment such as dishwashers, ovens, food warm-up
> equipment and so on that have varying levels of power consumption during
> operation (even PCs and laptops). We are sometimes using nameplate
> installed kW values, but deep inside we know that this is quite wrong -
> but we have no other more reliable source / guideline for such equipment.
> I would appreciate any feedbacks on how others are modelling such
> equipment.
>
> Thank you,
>
> Omer Moltay, LEED AP
> Mimta
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
More information about the Equest-users
mailing list