[Equest-users] External Wall Calculation

Bishop, Bill wbishop at pathfinder-ea.com
Wed Mar 17 13:38:46 PDT 2010


John,
 
You could try changing the value of infiltration in the wizard (which
allows cfm per sq. ft. of exterior wall). I can't find it in the
documentation but I assume that the value of cfm/ft2 for each space
(when using Air Change method) is calculated by eQUEST based on the
value of cfm/ft2 entered in the wizard. If you're already in DD Edit
mode, you'll have to work from a saved-as copy of your model (to go back
to the wizard) and work with the input files to copy the new
infiltration numbers. This might not be worth it unless you haven't made
a lot of changes to the spaces in DD Edit mode, or if you are good at
selective editing of input files.
 
Regards,
Bill 
 
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Grando,
John
Sent: Wednesday, March 17, 2010 4:10 PM
To: Scott Criswell
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] External Wall Calculation
 
Scott,
 
Thanks for the explanation, at least now I know I shouldn't bother
banging my head against the wall on this one.  Does anyone have any tips
for changing infiltration CFM/SF of exterior wall without going through
each zone and manually calculating it?
 

John Grando LEED AP| Mechanical Engineer

  
 
 
________________________________

From: Scott Criswell [mailto:scott.criswell at doe2.com] 
Sent: Wednesday, March 17, 2010 4:01 PM
To: Grando, John
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] External Wall Calculation
The DOE-2 BDL expression module does not allow parent components to
reference keyword values of their child components.  Back when the
expression module was developed, this limitation was put in place to
minimize changes required to the BDL file reading & defaulting mechanism
and also to simplify expression dependencies evaluation and minimize the
likelihood of circularities defined when two components can each
reference data of the other.
The ruleset processing mechanism that provides the foundation of the
compliance analysis and QC reporting features of eQUEST does include the
ability to reference components in both directions (children referencing
parents as well as parents referencing children), but to date this
capability has not been extended for use in performing parametric runs
or facilitating semi-automated edits to building models.

- Scott


Grando, John wrote: 
Hello All,
 
Does anyone know of a way I can reference a child code word?  My
specific situation is that I want my infiltration to be controlled via a
global parameter that represents the infiltration in terms of CFM/SF of
Exterior wall.  I want to be able to parametrically change this value so
I have to do it in DD Edit.  The problem is that infiltration is a zone
keyword that is the parent of the exterior wall.  It wouldn't be an
issue the other way around because I could just use the #P("keyword").
Any ideas on how I can reference the child using DOE2 language?
 
 
John Grando LEED AP| Mechanical Engineer
 
 
 

NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if
any) are intended solely for the use of the addressees hereof. In
addition, this message and the attachments (if any) may contain
information that is confidential, privileged and exempt from disclosure
under applicable law. If you are not the intended recipient of this
message, you are prohibited from reading, disclosing, reproducing,
distributing, disseminating or otherwise using this transmission.
Delivery of this message to any person other than the intended recipient
is not intended to waive any right or privilege. If you have received
this message in error, please promptly notify the sender by reply E-mail
and immediately delete this message from your system. 



________________________________



 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
  

NOTICE OF CONFIDENTIALITY This E-mail message and its attachments (if
any) are intended solely for the use of the addressees hereof. In
addition, this message and the attachments (if any) may contain
information that is confidential, privileged and exempt from disclosure
under applicable law. If you are not the intended recipient of this
message, you are prohibited from reading, disclosing, reproducing,
distributing, disseminating or otherwise using this transmission.
Delivery of this message to any person other than the intended recipient
is not intended to waive any right or privilege. If you have received
this message in error, please promptly notify the sender by reply E-mail
and immediately delete this message from your system. 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100317/a85218cf/attachment.htm>


More information about the Equest-users mailing list