[Equest-users] Existing building simulation

David S Eldridge DSE at grummanbutkus.com
Tue Mar 16 17:40:16 PDT 2010


Your model results have very little energy for fans and cooling (and basically no heating) - I'm not sure what you would calibrate.  The actual data seems to show a much more pronounced weather dependence.

Probably some rough hand-calcs to check against annual fan and cooling energy usage estimates might be a good place to verify your model inputs for the HVAC systems.  I think you have a little bit of debugging of the inputs to go before thinking about "fine tuning" or calibrating.

David
http://www.grummanbutkus.com



From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Vaziri, Mo (ON0F)
Sent: Tuesday, March 16, 2010 10:20 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Existing building simulation

If we are doing a simulation for an existing building and the actual electricity consumption does not match with the simulation, how can we adjust/calibrate it?

The snapshot shows the actual (blue graph) vs. simulation.

[cid:image001.gif at 01CAC521.9F3BCED0]

Regards,
Mo Vaziri

                                             Honeywell
Mo Vaziri, P. Eng. , LEED AP, CEM
Design Build / Energy Engineer
Honeywell Building Solutions - Canada
85 Enterprise Boulevard, Suite 100
Markham, Ontario, L6G 0B5
*       Phone: (289) 333-1340
*                 Fax:      (289) 333-1333
*       Cell:     (416) 527-4692
*       mohammad.vaziri at honeywell.com<mailto:pmohammad.vaziri at honeywell.com>



-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/dd4f41a5/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.gif
Type: image/gif
Size: 11977 bytes
Desc: image001.gif
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100316/dd4f41a5/attachment.gif>


More information about the Equest-users mailing list