[Equest-users] LEED modeling- Unit heaters

Bishop, Bill wbishop at pathfinder-ea.com
Thu Mar 11 13:01:23 PST 2010


Ana,
 
Since this is a residential building, your baseline system is PTAC (or
PTHP if you have electric heat in the proposed). So put PTACs in your
proposed model stairwells and mechanical rooms, with electric heat, and
using the fan power and cfm of your unit heaters. Create
stairwell/mechanical room cooling and heating thermostat schedules, with
the cooling thermostat high and the heating thermostat lower than your
living spaces. Then use the same thermostat schedules for proposed and
baseline.
 
Regards,
Bill
 
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.         
________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Ana N.
Sent: Thursday, March 11, 2010 3:44 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] LEED modeling- Unit heaters
 
Dear e-quest user,
 
I am sure this is a common case and many of you have modeled this
before. 
I have several spaces which are heated only with unit heaters (electric
heat). If there is no cooling, per ASHRAE Appendix G , the cooling in
proposed case should be the same as cooling in my baseline. How would
you model this? What type of system and what type of cooling should I
use in my propose and baseline?  This is a residential building, 170,000
s.f.  with non-residential area of about 45,000 s.f. Spaces I am talking
about are stairs and mechanical rooms. 
 
Thank you for sharing your expirince and advice.
 
Ana
________________________________

Hotmail: Trusted email with Microsoft's powerful SPAM protection. Sign
up now. <http://clk.atdmt.com/GBL/go/201469226/direct/01/> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100311/e348dfe7/attachment.htm>


More information about the Equest-users mailing list