[Equest-users] Changing System fromVAV System w/ Reheat to CAV w/No Reheat

Gaurav Mehta gmehta75 at gmail.com
Wed Mar 10 21:32:52 PST 2010


Robert,



1. Go to Fans/Flow Parameters/Set 'Min Flow Ratio' to 1. This will make sure that the air volume does not vary.

2. Go the the Heating tab under Coil Cap / Control, set the Zone Heat Source to 'Not Installed' then right click on Reheat Delta T and select Restore Default. That'll make the Reheat Delta T option grayed out. Now specify the Hot Deck Max Leaving Temp-- can be the same as Zone Entering Max. Supply Temp., it is the maximum temperature of air leaving the heating coils.

3. The other option would be to change the system type to Reheat Fan System and don't specify any reheat-as per 2 above.


Hope it helps.


Best regards,

Gaurav Mehta

Sustainable Building Analyst

Stantec




From: Robert Des Rosiers 
Sent: Wednesday, March 10, 2010 14:09
To: equest-users at lists.onebuilding.org 
Subject: [Equest-users] Changing System fromVAV System w/ Reheat to CAV w/No Reheat


All:

I am attempting to change my VAV system w/ reheat to a CAV system w/ no reheat.  I believe I have accomplished the change to constant volume by changing the 'fan control' of the AHU to 'constant volume'.  How do I remove any reheating from the previous VAV system?  Do I change the reheat delta T to zero?

 

Kindly,

 

Robert Des Rosiers, LEED-AP

STUDIO MA

130 N Central Avenue, No.300 Phoenix, Arizona 85004

Telephone 602 251 3800

Fax 602 251 3100

 



--------------------------------------------------------------------------------


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100310/643897fd/attachment.htm>


More information about the Equest-users mailing list