Hi Vikram and Rohini,
Thanks for the response.
Well, I see that on July/August, the Humidity levels are pretty high. So
in order to remove excess humidity in the air, the heater operates.
So that satisfies the heating energy levels.
But actually I am trying to find a correlation b/w the HVAC Power
consumption and Heat Index(Dry Bulb + Humidity) per month.
For statistical purposes, am finding the correlation between the Power
consumed and difference b/w the actual and the expected.
For eg. If my room temp is 72F, and outside the Heat Index is 90F,
Difference is 18F. Power Consumed is P1
If the outside temperature is 54F,
Difference is again 18F. Power consumed is P2.
And there is a huge difference, as P1> P2. Always. Anything to be altered
in the Heater Side of HVAC.
And also please let me know on how to nullify the humidity control of HVAC
in eQUEST! The wizards do not have an option. And am unable to find it in
the Detailed Edit.
Am unable to attach the project file,as it is approximately 18Mb. I will
upload it in a common area and will update you with the link!
Regards,
Siddharth Venkataraman
Tata Consultancy Services
Mailto: siddharth.v at tcs.com
Website: http://www.tcs.com
____________________________________________
Experience certainty. IT Services
Business Solutions
Outsourcing
____________________________________________
From:
"Sami, Vikram" <Vikram.Sami at perkinswill.com>
To:
R B <slv3sat at gmail.com>, Siddharth V <siddharth.v at tcs.com>
Cc:
equest-users <equest-users at lists.onebuilding.org>
Date:
06/29/10 06:58 PM
Subject:
RE: [Equest-users] HVAC simulation
To follow up on Rohini's comments:
If your lights and equipment are on the 12/7 schedule, and you have a
constant volume reheat then your supply volume is probably based on the
peak condition, and anything below is reheat. Did your cooling load also
go down drastically when you switched to 12/7 mode?
Could you attach an inp file?
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com
www.perkinswill.com
Perkins+Will. Ideas + buildings that honor the broader goals of society
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of R B
Sent: Tuesday, June 29, 2010 8:56 AM
To: Siddharth V
Cc: equest-users
Subject: Re: [Equest-users] HVAC simulation
Depends on what kind of system you are using. looks like there is some
kind of reheat going on in the night hours during summer.
-rohini
On 6/29/10, Siddharth V <siddharth.v at tcs.com> wrote:
> Hi,
>
> I am currently using eQUEST to simulate the performance of a building
(an
> ideal case), where in the HVAC operates at the below temperatures 24x7
for
> the whole year.
>
> Below are the preset values:
>
> Heat when temp <= 74F
>
> Cool when temp >= 76F
>
> Ideal temp of the building is 75F
>
> Also cool, when the outside temp >=72F
>
>
> Error in Simulation:
>
> I always see that the total heating power consumed in Jan/Dec month
> (Winter) is lesser than that July and August Month (Summers).
>
> But the simulation's outside Dry Bulb Temperature (avg, min and max
> Temperature) is higher during July/August when compared to Jan/Dec
month.
>
>
> If I operate the HVAC for 12x7 (7am to 7pm) for all the days, then it
> follows the seasonal pattern (heating power is higher in Jan/Dec than
> Jul/Aug).
>
> But I need to get the power O/P when it operates for 24x7 only!
>
> Please let me know as to why this error introduced, and how to rectify
it!
> Or must I add some more details in the detailed edit.
>
>
>
> Regards,
> Siddharth Venkatraraman
> Tata Consultancy Services
> Mailto: siddharth.v at tcs.com
> Website: http://www.tcs.com
> ____________________________________________
> Experience certainty. IT Services
> Business Solutions
> Outsourcing
> ____________________________________________
> =====-----=====-----=====
> Notice: The information contained in this e-mail
> message and/or attachments to it may contain
> confidential or privileged information. If you are
> not the intended recipient, any dissemination, use,
> review, distribution, printing or copying of the
> information contained in this e-mail message
> and/or attachments to it are strictly prohibited. If
> you have received this communication in error,
> please notify us by reply e-mail or telephone and
> immediately and permanently delete the message
> and any attachments. Thank you
>
>
>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
This email and any files transmitted with it are confidential and intended
solely for the addressee. If you are not the named addressee you should
not disseminate, distribute, copy, or alter this email.
=====-----=====-----=====
Notice: The information contained in this e-mail
message and/or attachments to it may contain
confidential or privileged information. If you are
not the intended recipient, any dissemination, use,
review, distribution, printing or copying of the
information contained in this e-mail message
and/or attachments to it are strictly prohibited. If
you have received this communication in error,
please notify us by reply e-mail or telephone and
immediately and permanently delete the message
and any attachments. Thank you