[Equest-users] Waterside Economizer
Sami, Vikram
Vikram.Sami at perkinswill.com
Mon Jun 28 11:58:29 PDT 2010
I do have a question about that - point # 1 - A water-side economizer cannot precool the return flow prior to entering the chillers.
I might be showing my ignorance here, but - isn't that what the cooling tower does? So if you have a CHW loop with two chillers attached - a normal (lets say centrifugal) chiller and a water side economizer. When the water side economizer cannot satisfy all the load, it would switch completely to the centrifugal. However - wouldn't the cooling tower still be used as a heat rejection to " precool the return flow prior to entering the chillers"? In which case is point 1 not really a shortcoming?
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: Howe, Timothy [mailto:Timothy.Howe at stantec.com]
Sent: Monday, June 28, 2010 2:49 PM
To: Sami, Vikram; Varkie C Thomas
Cc: Sethi, Amarpreet; equest-users at lists.onebuilding.org; Jonathan Smith
Subject: RE: [Equest-users] Waterside Economizer
The only problem is this:
[cid:image001.png at 01CB16D2.35834650]
Timothy Howe, MS, LEED® AP
Mechanical Engineer
Stantec
2060 Brighton-Henrietta Town Line Road
Rochester NY 14623-2792
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 330-8681
stantec.com<http://www.stantec.com>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
ü Please consider the environment before printing this email.
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Sami, Vikram
Sent: Monday, June 28, 2010 2:44 PM
To: Varkie C Thomas
Cc: Sethi, Amarpreet; equest-users at lists.onebuilding.org; Jonathan Smith
Subject: Re: [Equest-users] Waterside Economizer
Varkie,
Which version of eQUEST are you using? If it's a new version then you should be able to model it as a chiller. See attached documentation - pg 68 (73 of the PDF)
Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462 f: 404.892.5823 e: vikram.sami at perkinswill.com www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will. Ideas + buildings that honor the broader goals of society
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Varkie C Thomas
Sent: Monday, June 28, 2010 1:08 PM
To: Varkie C Thomas
Cc: Sethi, Amarpreet; equest-users at lists.onebuilding.org; Jonathan Smith
Subject: Re: [Equest-users] Waterside Economizer
I am having a hard time getting �Chiller Type = Waterside Economizer� to work in eQ. I received 2 messages recommending this as the solution. I have 2 more saying that they have not been able to model WSE in eQ. Please let me know if it is not supposed to work.
Unlike DOE2.1E this is the only minimum input required in eQ. In this project during WSE operation we require a Clg-Twr leaving temp (Plate & Frame HX entering temp) of 42F so that the CHW temp leaving the HX is 44F or 46F. The eQ default is 85F. Even with this default and �Chiller Type = Waterside Economizer� I get the error message �Condenser Water Loop has Zero Design Flow�.
Unlike DOE2.1E there is no way of attaching a schedule for WSE operation. I have attached eQ input-output �Without-WSE-1� and �With-WSE-2�; DOE2.1E definitions of WSE commands and keywords; a sample DOE2.1E plant section input showing WSE; a schematic of Plate & Frame HX; and my eQ input for WSE and the resulting error message. The attached project is dummy to test eQ for WSE.
Has anyone modeled WSE with eQ? WSE works with DOE2.1E commands and keywords. Does Waterside Economizer work with EnergyPlus (this project is also going to be modeled with E+ using Design-Builder interface for building and systems), TRACE or HAP
Varkie
This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100628/5aa249a3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 47031 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100628/5aa249a3/attachment.png>
More information about the Equest-users
mailing list