[Equest-users] Help - Manipulating dedicated gas consumptions in eQUEST
Bishop, Bill
wbishop at pathfinder-ea.com
Wed Jun 23 13:43:13 PDT 2010
Vaughn,
Rumor has it that eQUEST v4.0 will have an "Autotweek" tool. You tell
the program what the output should be, and the inputs are automatically
adjusted accordingly. :-)
Kidding aside, why do you need eQUEST to tell you what you already
"know" from your spreadsheet? Matching the total BTUs does not mean much
if the individual values for space heating, DHW and process loads are
all way off.
You can adjust the DHW by adjusting the Process Flow (gpm) for the DHW
loop or by adjusting the process load schedule.
You can adjust the Input Power (Btu/h) and schedules for any gas loads
that you enter as Internal Energy Sources in your spaces.
If gas loads are entered as Direct - Interior or Direct - Exterior loads
on your fuel meter, then change the load (MBtu/h) or schedule in the
Utility & Economics module for the meter.
Space heating gas consumption is not so direct. There are many things
that affect this, including thermostat schedules, boiler efficiency,
building envelope, miscellaneous loads, lighting power, occupancy,
outside air, economizer operation, and nighttime fan operation, just to
get you started. Many of these also affect your electrical consumption.
Hopefully that's not on your spreadsheet too.
Long story short - model calibration is not so simple. Start crunching!
Regards,
Bill
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Synergy
Team
Sent: Wednesday, June 23, 2010 1:24 PM
To: eQUEST-users at onebuilding.org
Subject: [Equest-users] Help - Manipulating dedicated gas consumptions
ineQUEST
good afternoon everyone,
We are modelling a 2 story multi-family structure in eQuest that
contains four 3 bedroom apartments side by side. After simulating the
model, we have found that the eQuest estimate for TOTAL gas consumption
(space heating + DHW + misc. equipment) is very close to our spreadsheet
calculation. The model indicates a total annual gas consumption of
413.14 Million Btu's. We calculated 414.01 Million Btu's. Very close!
However, the proportions of Btu's dedicated to space heating, DHW, and
misc equipment is very different in our eQuest model and our
spreadsheet. Does anyone know a simple way to manipulate the proportions
of Btu's dedicated to each of these three categories without affecting
the TOTAL annual gas consumption which is nearly dead on? We would like
to divy it up based on our calculated usage patterns. We understand that
this might be accomplished by adjusting the numbers in the Space
Heating/DHW boiler diagrams. Also, that changing the daily/weekly
schedules might affect this. Are these the only ways to approach this or
is there a more simple solution without having to crunch such numbers?
Thanks.
Vaughn Slovak
Architectural Designer
Synergy Design
p.845.255.1733
f.845.255.1694
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100623/45a5ebfb/attachment.htm>
More information about the Equest-users
mailing list