[Equest-users] eQuest: SEER to EIR??
Josh Greenfield
JGreenfield at primerachicago.com
Tue Jun 15 13:01:43 PDT 2010
Sorry to be beating a dead horse...
the attached document has been floating around the boards for awhile in
regards to how an entered EER value in the Wizard gets converted to the
Cooling-EIR value in the Detailed Edit mode, and after doing a few EER
value tests, I can confirm it works...
I've also found in various emails the conversions on the heat pump
heating side of COP and HSPF to Heating-EIR, and those work too after
testing various values in the Wizard...
Heating EIR = (1/(COP*3.413)-0.012167)/((1/3.413)-0.012167)
Heating EIR = (1/((HSPF*0.28+1.13)*3.413)-0.012167)/((1/3.413)-0.012167)
But I just can't get the SEER to EER conversion from the document (EER =
SEER x 0.778 + 1.4) to work. I'm assuming that the converted SEER to
EER value then gets put into the working equation from that PDF of
Cooling-EIR = ((1/EER)-0.12167)/((1/3.413)+0.012167)).
As an example...if you put in a 13 SEER into the Wizard, a 0.2507
Cooling-EIR value is calculated in the Detailed Edit mode, but if you
use the SEER to EER (13 SEER would equal a 11.514 EER) and then the EER
to EIR equations, it says EIR should be 0.2447.
Any help/suggestions would be great...hopefully it's just a math error
on my part.
Josh Greenfield, PE, REP, LEED AP
Energy Services Manager
Associate Vice President
312.242.6392 Direct
jgreenfield at primerachicago.com
<blocked::mailto:jgreenfield at primerachicago.com>
Primera Engineers, Ltd.
100 S. Wacker Drive, Suite 700
Chicago, IL 60606
312.606.0910 Main
312.606.0415 Fax
http://www.primerachicago.com <http://www.primerachicago.com>
#####################################################################################
This e-mail message has been scanned for Viruses and Content and cleared
by MailMarshal
#####################################################################################
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100615/1534da6d/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1879 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100615/1534da6d/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Converting EER and SEER to Cooing EIR.PDF
Type: application/octet-stream
Size: 92460 bytes
Desc: Converting EER and SEER to Cooing EIR.PDF
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100615/1534da6d/attachment.obj>
More information about the Equest-users
mailing list