[Equest-users] Baseline Modeling
Paul Buchheit
paul.buchheit at eesinet.com
Fri Jun 11 10:22:45 PDT 2010
Hello Omar,
These are the steps I suggest you follow to complete the proposed building and the baseline building models most efficiently:
1) Model the proposed building first. Do everything you can in wizard. Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.
2) Save two new copies of your model- one for the proposed model to be completed in the detailed editor and one for the baseline model.
3) Complete the proposed model in detail editor
4) Go back to the model you saved in step 2 of this process as the baseline model and change your selections in the wizard to comply with ASHRAE 90.1. This is quicker and easier than changing all the values manually.Keep a copy of the model at this stage so that you can easily go back to this state of your model if necessary.
5) Save a new copy of the baseline model and complete it in the detailed editor.
This process allows you to do everything you can in the wizard for both the baseline and proposed building models. It also helps to ensure that schedules and other aspects shared by the two buildings are modeled the same as required by ASHRAE 90.1.
I hope this helps,
Paul
Paul Buchheit
Mechanical Engineer
EESI
phone: 541-754-1062
fax: 541-753-3948
paul.buchheit at eesinet.com
----- Original Message -----
From: Peter Hillermann
To: 'Omar Katanani' ; equest-users at lists.onebuilding.org
Sent: Friday, June 11, 2010 9:26 AM
Subject: Re: [Equest-users] Baseline Modeling
Omar,
You need to start with the baseline then enter you efficient values. Yes you need to enter ASHRAE standards manually.
Thanks,
PETER HILLERMANN
peterh at westallarchitects.com
westall
architects
3404 pierce drive
chamblee, georgia 30341
o 770.458.4113
f 770.458.5352
c 678.898.2936
westallarchitects.com
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Katanani
Sent: Friday, June 11, 2010 11:48 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Modeling
Dear all,
I am modeling a school using eQUEST. I have entered the values corresponding to the proposed building (like the specifications given). I would like to model the baseline building according to ASHRAE 90.1 standard.
Do I have to change the U-values, HVAC strategy, Window/wall ratio, and the other stuff manually? That is, shall I open the ASHRAE standard and start changing all values one-by-one? The ASHRAE Standard 90.1 isn't recognized by eQUEST such that it can create the baseline case alone? That would save a lot of time!
Best regards,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Chawkatly Building (Valli & Valli), 6th floor
Charles Helou Street, Saifi District
Beirut, Lebanon
Mobile: +961 (0) 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0) 207 939 0989
Fax: +44 (0) 207 939 0981
Website: www.ecoconsulting.net
------------------------------------------------------------------------------
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 3224 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 2436 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment.gif>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 27542 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/e26bd9b8/attachment-0001.jpeg>
More information about the Equest-users
mailing list