[Equest-users] Excessive Unmet Heating Load Hours with anAuto-Sized HVAC System
Li, Lan
lli at sbmce.com
Fri Jun 11 10:01:20 PDT 2010
Pahsa,
Will you revise your design at this time?
Thanks!
Lan
Lan Li, PE
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 123
Cell: (330) 904-6292
Fax: (330) 896-9180
lli at sbmce.com
www.sbmce.com <http://www.sbmce.com/>
Columbus Branch Office (614) 448-1498
* Please consider the environment before printing this email.
This e-mail (including any attachments) is confidential and may be
legally privileged. If you are not an intended recipient or an
authorized representative of an intended recipient, you are prohibited
from using, copying or distributing the information in this e-mail or
its attachments. If you have received this e-mail in error, please
notify the sender immediately by return e-mail and delete all copies of
this message and any attachments.
Thank you
________________________________
From: Pasha Korber-Gonzalez [mailto:pasha.pkconsulting at gmail.com]
Sent: Thursday, June 10, 2010 10:55 PM
To: Robert Des Rosiers
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Excessive Unmet Heating Load Hours with
anAuto-Sized HVAC System
I have found with my own projects that even sometimes when the HVAC
designer has specified a specific capacity for htg water equipment that
sometime in my model file I still have unmet loads for htg. I suggest
at this point specify additional htg capacity by either increasing the
reheat delta-T from say 30F to 50F and/or adding zone level baseboards.
By adding the baseboards you are adding a component of the system that
will supplement the skin losses being experienced by the simulation
model.
by adding baseboards for the additional requrired heat then you should
be able to meet your heating loads.
hope this helps,
pasha
On Thu, Jun 10, 2010 at 7:38 PM, Robert Des Rosiers
<desrosiers at studioma.com> wrote:
All:
I have completed an energy model for a baseline scenario from which to
compare my proposed design. The baseline HVAC system is a constant
volume single zone AHU w/ no reheat; the AHU is served by HW and CHW
loop from a central plant. I have set this up in eQuest as a "Variable
Air Volume" system type with the AHU fan control set to "Constant
Volume"; my thought here is that each zone fed by the AHU will control
temperature using a VAV box w/ no local reheat or cooling. Flow and
temperature from the AHU will be delivered based on the coolest or
warmest zone it serves.
All seems fine with the design flows, ventilation flows and cooling
capacities. My problem is with the heating capacity as I have excessive
unmet heating hours (50,000). I have allowed eQuest to size the heating
capacity of the preheat and heating coil as well as the minimum flow
ratios. Does anyone have any thoughts as to what is causing these unmet
heating load hours? Is the way I have set-up the desired baseline HVAC
system incorrect?
Any guidance is greatly appreciated. Thanks -
Robert Des Rosiers, LEED-AP
STUDIO MA
130 N Central Avenue, No.300 Phoenix, Arizona 85004
Telephone 602 251 3800
Fax 602 251 3100
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/f68c2e57/attachment.htm>
More information about the Equest-users
mailing list