[Equest-users] Space has no ZONE - one is required
Bishop, Bill
wbishop at pathfinder-ea.com
Fri Jun 11 06:07:38 PDT 2010
Omar,
Your spaces and zones are initially created in the wizard in screen two
of the building shell. A space will be created for each zone that you
define. If you create a new space in DD Edit mode, you will have to
create a new zone for it per Rob's instruction. Assign the new zone to
the errant space and to a system from the Basic Specifications tab of
the zone.
Regards,
Bill
William Bishop, EIT, BEMP, LEED(r) AP | Pathfinder Engineers &
Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob
Hudson
Sent: Friday, June 11, 2010 8:48 AM
To: Omar Katanani
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Space has no ZONE - one is required
you'll need to go to the HVAC section of the Detailed Design mode of
your project and create a new thermal zone by right clicking on an
existing one and select "create new thermal zone." Then either assign
it to an existing system or create a new one.
On Fri, Jun 11, 2010 at 8:18 AM, Omar Katanani <omar at ecoconsulting.net>
wrote:
Dear all,
I am having the error: "Space has no Zone - one is required". Can
someone tell me:
1- What does this error mean?
2- How can I fix it (what should be done and from where)?
3- How do you "create a zone" after you have created a Space and its
walls?
Many thanks,
Omar
___________________________
Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net
EcoConsulting (Lebanon)
Chawkatly Building (Valli & Valli), 6th floor
Charles Helou Street, Saifi District
Beirut, Lebanon
Mobile: +961 3 045 045
EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0)207 939 0989
Fax: +44 (0)207 939 0981
Website: www.ecoconsulting.net
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
--
Rob Hudson
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100611/323edc86/attachment.htm>
More information about the Equest-users
mailing list