[Equest-users] Water to water heat pump
Pasha Korber-Gonzalez
pasha.pkconsulting at gmail.com
Wed Jun 9 10:30:53 PDT 2010
Jason,
you need to be in ddedit mode, go to the "plant" tab (aka water-side tab).
Once in this screen click your mouse on the very top line in your project
tree at the left where it has your project name. Right click your mouse on
the project name and you will see a new window open that lets you select a
type of equipment that you would like to add.
For your choice, choose "add a chiller", then select the chiller of type
water-to-water hp. It will then ask you which loops you will be connecting
too. You will need to have a circulation loop of type "lake/well" created
in order to connect your heat rejection side of the Water-to-water HP. then
you can also link to the CHW & HW loops for your system supply.
see attached screen shot of how to add a new chiller.
Pasha
On Wed, Jun 9, 2010 at 10:49 AM, Scalera, Jason <jscalera at psands.com> wrote:
> Hi all,
>
> I am trying to model a system which uses a water to water heat pump running
> off of a GSHP water loop to preheat the water for the domestic hot water
> heater, but I can't seem to find any way to do so. The GSHP is also being
> used to supply another set of heat pumps for some suites. I'm a new user to
> eQUEST but I've spent some time reading these forums. Any ideas?
>
> Thanks
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100609/cbe84a93/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: screen shot.docx
Type: application/vnd.openxmlformats-officedocument.wordprocessingml.document
Size: 94695 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100609/cbe84a93/attachment.bin>
More information about the Equest-users
mailing list