[Equest-users] Ashrae Baseline Model & Unmet loads

Dakota Kelley dakotak at teliospc.com
Wed Jul 21 13:23:56 PDT 2010


Amanda,

 

The main problem is the mechanical penthouse where you’re supplying at 70 F to maintain 90 F.  The indoor sizing temp and hourly T-stat setting were the same, which I admit sounds fine in theory.  However, in terms of eQUEST auto-sizing, the resulting airflow will just barely be enough – it will not be sufficient during peak months as indicated by the high number of unmet load hours (nearly all of which were occurring in July and August).   The 1.25 cooling sizing ratio is for coil capacity, but that does not help in terms of airflow, and insufficient airflow is nearly always the cause of unmet loads (I have discussed the opposing nature of sections G3.1.2.2 and G3.1.2.8 here: http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2010-January/003024.html).  You’re right that it’s usually a control issue, but this case is a little different because your system is on 24/7 to maintain a constant temperature.  This is why night cycling did not make a difference. 

 

Before going further, it may be beneficial to take a look at G3.1.1 exception b.  I think the mechanical floor may qualify.  However, the entire baseline system does not appear to follow Table G3.1.1A; the inclusion of CHW and steam meters implies a district thermal system.  I’ll accept what I see at face value without a deeper understanding of the design.  However, as noted in the bullets below, I believe you’re trying to model System 7.

 

In the attached project I made the following changes to AHU-504, the one serving the mechanical floor.  Note that only the first two modifications were necessary to eliminate all unmet cooling hours, the rest are simply to incorporate different sections of Appx G:

 

·         Set indoor cooling design temp to 80F with 60F supply temperature, but hourly T-stat setting was left at 90 F.  You’ll note that this increased the supply air CFM by about 13%.  If 80F/60F is too far off from the proposed design, try gradually increasing the design temp back up toward 90F with the same delta T until the unmet hours start appearing again.  If you’re trying to maintain 90F, I would assume the proposed system was at least designed with a little buffer, maybe 85F or something in that range. 

·         Set indoor heating design temp to 65 F and a Zone Entering Max Supply Temp to 85F for the same reason as described above – you want at least a few degrees buffer between the design temp and hourly T-stat temps.  This introduces 65F unmet heating hours to EL3 South Perim Zn (G.S12), but I don’t think this is a real zone unless the architect is into 87 SQFT triangular rooms.  It appears to be a byproduct of trying to achieve the 3rd floor’s custom footprint.  If you cleaned up the building geometry, these hours would go away.  To illustrate, I added two Air Walls to this zone with the proper NEXT-TO spaces defined, and the unmet heating hours were eliminated.     

·         Changed the CHW and HW valves from three-way to two-way (the building is small enough that the CHW & HW pumps should be riding their curves per G.3.1.3.5 and G3.1.3.10, and the pumps were already set to one-speed).

·         Set Max Cooling Reset Temp to 65F and Min Cooling Reset Temp to 60F (for a design supply of 60F) per G3.1.3.12.  Originally it was set to a Zone Entering Min Supply Temp of 70F and a Max Cooling Reset Temp of 50F, which don’t agree with each other.

·         Ensured all conditioned zones under AHU-504 have a heating and cooling schedule assigned, the same design temps, the same thermostat type, and the same 6F throttling range.  There was a mix of different conditions, which I assume was a result of trying to address unmet hours.

·         Restored default under the Heating/Unitary Power/Furnace section (there is no furnace).  However, I was confused by the inclusion of HW coils in the AHU and electric zone reheat.  Is this supposed to be System 7 or System 8?  The standard VAV terminal units and water-side configuration imply System 7, so I set the Heat Source to “Not Installed” and the Zone Heat Source to “Hot Water Loop”.

·         Set the Hot Water Loop operation to “Demand” (there’s nothing in Appx G that says it must be on Demand, but Standby is not a realistic secondary loop operation and a good LEED reviewer will call you on it)

·         Reversed the high/low temps in schedule “Reset temp HWday” – they were backwards from what G3.1.3.4 indicates.

 

Try following the above on the other systems and see what it does for your unmet hours.  Let me know if you have any questions or concerns about what I did.

 

Thanks,

 

 

  
                                

DAKOTA KELLEY 

Project Designer | Energy Analyst

                          

                              Office: 214.744.6199                 

                              Cell: 214.280.3825

                              Fax: 214.744.0770    

 

http://www.teliospc.com <http://www.teliospc.com/>          3535 Travis St. Suite 115

dakotak at teliospc.com            Dallas, TX 75204                                                     

                                

| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |

 

CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed, 

And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you

are not the intended recipient, please email the sender immediately, and delete this email from all computers.  Any 

distribution or other use is strictly prohibited.  Copyright © 2009 Telios Corporation.

 

 

 

 

 

 

 

From: Martz, Amanda [mailto:amartz at klingstubbins.com] 
Sent: Wednesday, July 21, 2010 12:30 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Ashrae Baseline Model & Unmet loads

 

I have reverse action set, a range of 6 degrees, night cycling set to “cycle on any,” and a 20 degree delta T. You’re right, those usually do the trick, that’s why I’m so stumped. 

 

________________________________

From: Amber Welsh [mailto:amber at timmonsdesigneng.com] 
Sent: Wednesday, July 21, 2010 1:28 PM
To: Martz, Amanda
Subject: RE: [Equest-users] Ashrae Baseline Model & Unmet loads

 

Amanda,

 

When I first had these problems it had to do with fan control and night cycling.  Make sure that your fans are cycling.  Next, check to make sure that you have a minimum delta T of 20 between room set point and supply air temperature.  These are the 2 biggest things affecting the unmet hours.

 

Amber

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Martz, Amanda
Sent: Wednesday, July 21, 2010 1:22 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Ashrae Baseline Model & Unmet loads

 

I have several VAV units with reheat serving several zones in my Ashrae baseline model. It is autosizing all of the capacities, so why would I have unmet loads? I have cooling and heating set to size at 1.15 and 1.25 as Ashrae states, and I have cooling control set to “warmest.” I’m sure it is a control issue, but I can’t figure out what exactly it is. I attached my model, any help would be very greatly appreciated!

 

Amanda E. Martz, EIT, LEED AP

Mechanical Engineer

KlingStubbins

2301 Chestnut Street
Philadelphia, Pennsylvania
19103

P 215.569.2900, ext. 3612

F 215.569.5963
E amartz at klingstubbins.com 
W www.klingstubbins.com <http://www.klingstubbins.com/> 

 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100721/6ee11739/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100721/6ee11739/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2143 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100721/6ee11739/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Merck QO Detailed 7-21-2010 baseline meters.inp
Type: application/octet-stream
Size: 379691 bytes
Desc: Merck QO Detailed 7-21-2010 baseline meters.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100721/6ee11739/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Merck QO Detailed 7-21-2010 baseline meters.pd2
Type: application/octet-stream
Size: 109546 bytes
Desc: Merck QO Detailed 7-21-2010 baseline meters.pd2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100721/6ee11739/attachment-0001.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Merck QO Detailed 7-21-2010 baseline meters.pdl
Type: application/octet-stream
Size: 463017 bytes
Desc: Merck QO Detailed 7-21-2010 baseline meters.pdl
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100721/6ee11739/attachment-0002.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Merck QO Detailed 7-21-2010 baseline meters.prd
Type: application/octet-stream
Size: 1085 bytes
Desc: Merck QO Detailed 7-21-2010 baseline meters.prd
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100721/6ee11739/attachment-0003.obj>


More information about the Equest-users mailing list