[Equest-users] Coincident heating/cooling hours

Bishop, Bill wbishop at pathfinder-ea.com
Thu Jul 15 07:58:34 PDT 2010


Amanda,
 
The floating hours are hours when no heating or cooling is provided.
These are not related to unmet hours and you shouldn't try to "fix"
them. Coincident hours are when the system has simultaneous heating and
cooling loads. I believe a VAV w/reheat system will have coincident
hours whenever you are in cooling mode and have reheat coil loads.
 
Any time you have questions about reports, look in the eQUEST help menu
and look under DOE-2 Help -> Volume 4 -> Reports.
 
Regards,
Bill
 
William Bishop, PE, BEMP, LEED(r) AP | Pathfinder Engineers & Architects
LLP
Mechanical Engineer
 
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Sustainability - less is more.
________________________________

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Martz,
Amanda
Sent: Thursday, July 15, 2010 10:40 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Coincident heating/cooling hours
 
I have a 3 story building with 4 air handling units (vav & reheat) and
several AC units & fan coil units. In my ASHRAE baseline model, all of
my AHUs (according to report SS-C) have thousands of coincident heating
& cooling hours and lots of "floating" hours. Do floating hours mean
unmet hours? How do I fix coincident hours?
I've played with the cooling coil reset temps, cool control, throttling
range and anything else I can think of but don't see a fix. I can't
change cooling and reheat setpoints because of the ashrae 20 degree
delta t requirement. Thanks for any help!
 
Amanda E. Martz, EIT, LEED AP
Mechanical Engineer
KlingStubbins
2301 Chestnut Street
Philadelphia, Pennsylvania
19103
P 215.569.2900, ext. 3612
F 215.569.5963
E amartz at klingstubbins.com 
W www.klingstubbins.com <http://www.klingstubbins.com/> 
 
 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100715/85d6d585/attachment.htm>


More information about the Equest-users mailing list