[Equest-users] Lighting Control - Occupancy Sensor

Demba Ndiaye Demba.Ndiaye at setty.com
Mon Jul 12 12:41:02 PDT 2010


Reducing the installed LPD or reducing the schedules by the same percentages yield the same results. However, it is far easier to just reduce the LPD.

______________
Demba NDIAYE

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Li, Lan
Sent: Monday, July 12, 2010 2:36 PM
To: Carol Gardner; Nick Caton
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Lighting Control - Occupancy Sensor

 "User's Manual for ANSI/ASHRAE/IESNA standard 90.1-2004" page G-18  says " Occupant sensors alone for a combination of occupancy sensors and programmable timing controls have a 15% power adjustment factor for daytime occupancies and building less than or equal to 4000 ft^2. The power adjustment factor is 10% for all other  buildings. "  I think the key is " Power adjustment factor".  Please advise if my understanding is right.

Thanks!

Lan



Lan Li, PE
Mechanical Engineer
Scheeser Buckley Mayfield LLC
1540 Corporate Woods Parkway
Uniontown, OH 44685
Phone: (330) 896-4664 ext. 123
Cell: (330) 904-6292
Fax: (330) 896-9180
lli at sbmce.com<mailto:lli at sbmce.com>
www.sbmce.com<http://www.sbmce.com/>

Columbus Branch Office (614) 448-1498
 Please consider the environment before printing this email.
This e-mail (including any attachments) is confidential and may be legally privileged. If you are not an intended recipient or an authorized representative of an intended recipient, you are prohibited from using, copying or distributing the information in this e-mail or its attachments. If you have received this e-mail in error, please notify the sender immediately by return e-mail and delete all copies of this message and any attachments.
Thank you
________________________________
From: Carol Gardner [mailto:cmg750 at gmail.com]
Sent: Monday, July 12, 2010 12:46 PM
To: Nick Caton
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Lighting Control - Occupancy Sensor

Nick,

For occupancy sensors, I have always reduced the % on in the lighting schedules, never the installed LPD. Here's a thread from way back discussing how to do this:http://www.gard.com/ml/bldg-sim-archive/msg02168.html.

If the methodology has changed to reducing the LPD by 15% I'd like to know. It would be much easier and I'd love to be wrong!

How are others doing this?

Carol
On Mon, Jul 12, 2010 at 7:42 AM, Nick Caton <ncaton at smithboucher.com<mailto:ncaton at smithboucher.com>> wrote:
A small correction - the reduction (0-15%) is modifying the installed LPD (W/SF), not the schedules.  The reduction amount does vary based on the table Carol referenced in 90.1 Appendix G.

This is easiest to do in the wizards: there's an overall multiplier, defaulted to 1.00, on the bottom of lighting load screen.  In detailed it would require you to modify the space LPD values in the spreadsheet view, under the Internal Loads tab.

Agreeing with Carol's premise though - the way your question is worded suggests you weren't clear on the contents Appendix G.  For your own sake, definitely avoid relying on others to tell you what's within 90.1 or you might find yourself in hot water down the road ;).

~Nick

[cid:image001.jpg at 01CB21D8.A2028DC0]

NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com<http://www.smithboucher.com>

From: equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org> [mailto:equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>] On Behalf Of Carol Gardner
Sent: Sunday, July 11, 2010 5:27 PM
To: Derek Huang
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Lighting Control - Occupancy Sensor

For the spaces that don't require occupancy sensors you can show savings by modifying the lighting schedule. I think a 15% reduction is allowed, but verify that by looking in Appendix G where it tells you what you can do and when. In fact it would be good for you to make a practice of researching the answers to these types of questions yourself and save the more complicated questions for the listserv. It is important to respect everyone's time and do diligence by trying to find the answers yourself. I know it's a lot to process at first but you will benefit from the study.

Regards,
Carol
On Sat, Jul 10, 2010 at 6:21 PM, Derek Huang <Derek.Huang at atce.com<mailto:Derek.Huang at atce.com>> wrote:
Does anyone know if there is a spot for Occupancy Sensor lighting controls ? In both of DD Wizard mode and Detailed Data Edit mode, I didn't see any.

Thanks,

Derek Huang, LEED AP, CPD
Mechanical Engineer

Error! Filename not specified.

97 E. Brokaw Road, No 300
San Jose, CA 95112
Direct: 408 487-1305
Fax:      408 436-1511
www.atce.com<http://www.atce.com/>
derek.huang at atce.com<mailto:derek.huang at atce.com>



_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>



--
Carol Gardner PE



--
Carol Gardner PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100712/79b6dd0e/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100712/79b6dd0e/attachment.jpg>


More information about the Equest-users mailing list