[Equest-users] Strange errors in file- HELP!

Matthew W. Higgins MWHiggins at bpce.com
Fri Jul 9 08:38:11 PDT 2010


I've had this happen before as well. What I did was look at the PD2 file as a text doc and checked to see what the reference was coming from, in your case, lines 14898, 15237, and 15377. It seems like this may be zones that are looking for spaces to belong to and you may be able to just get rid of the zones, if they're non-existent.

Matthew Higgins, ASHRAE-HBDP, LEED-AP
Energy Engineer

Bridgers & Paxton Consulting Engineers, Inc.
4600-C Montgomery Blvd. NE
Albuquerque, NM  87109
505-883-4111
505-888-1436  Fax
mwhiggins at bpce.com

www.bpce.com

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Paul Brooks
Sent: Friday, July 09, 2010 9:33 AM
To: eQuest user forum
Subject: [Equest-users] Strange errors in file- HELP!

I am modeling an addition to an existing building.  I originally did the shell/zoning using just the original building.  I then, after saving a back up copy of the base building, i went back to the shell and zone drawing screens in the DD wizard and expanded the shell to account for the addition, and then went into the zone creation and adjusted my zones.  I was sure to follow the rules about matching verticies, etc.

Now i am getting errors concerning the zone and plenum.  It appears that the program is still seeing plenums and walls that are now non-existent.  The program says that plenums are being referenced but are not defined (see error message below).

Anyone got any ideas on how to clear this?






*ERROR****************************************************************************************

*ERROR*****EL3 East Perim Plnm (G.E6) was referenced on line 14898 but never

            defined.

*ERROR****************************************************************************************

*ERROR*****EL3 West Perim Spc (G.W4) was referenced on line 15237 but never

            defined.

*ERROR****************************************************************************************

*ERROR*****EL3 WNW Perim Plnm (G.WNW7) was referenced on line 15377 but never

            defined.





****************************************    5 ERRORS

****************************************    2 WARNINGS

****************************************  103 CAUTIONS

     *20195* COMPUTE ..

     *20196* STOP ..

****************************************    5 ABORT-LEVEL DIAGNOSTICS






-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100709/f27fffa8/attachment.htm>


More information about the Equest-users mailing list