[Equest-users] Appendix G - Fan schedules

Sami, Vikram Vikram.Sami at perkinswill.com
Thu Jul 8 09:46:28 PDT 2010


You access that in the detailed edit mode under night cycle control fr your fans.


STAY-OFF                    The fans stay off regardless of conditions.

CYCLE-ON-ANY            The fans are cycled on for the hour if the temperature of any zone in the system falls below the throttling range for heating,

CYCLE-ON-FIRST         The fans are cycled on for the hour if the temperature in the system's control zone falls below the throttling range for heating.

ZONE-FANS-ONLY        For a PIU system, the main or central system PIU fan will remain off but the individual zone terminal fans will cycle on separately to satisfy the heating setback temperature for each zone.


Vikram Sami, LEED AP
Sustainable Design Analyst
1382 Peachtree St. NE, Atlanta, GA 30309
t: 404-443-7462    f: 404.892.5823       e: vikram.sami at perkinswill.com   www.perkinswill.com<http://www.perkinswill.com/>
Perkins+Will.  Ideas + buildings that honor the broader goals of society


From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Omar Katanani
Sent: Thursday, July 08, 2010 12:37 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Appendix G - Fan schedules



Dear all,

ASHRAE 90.1 appendix G states that:

"Schedules for HVAC fans that provide outdoor air for ventilation shall run continuously whenever spaces are occupied and shall be cycled on and off to meet heating and cooling loads during unoccupied hours."

Can someone please explain to me how to do this? What type of schedule (1 or 2 schedules, etc.)

Thank you very much!

Best,
Omar
___________________________

Omar Katanani
Sustainable Design Engineer
Email: omar at ecoconsulting.net


EcoConsulting (Lebanon)
Nahas Building, 4th floor
4 St-Maron Street / Georges Haddad Avenue
Postal Code: 2028 5806 SAIFI
Beirut, Lebanon
Tel:       +961 (0) 1 971 255
Mobile:    +961 (0) 3 045 045


EcoConsulting (UK) Ltd
28 Marshalsea Road
London, SE1 1HF
Tel: +44 (0)207 939 0989
Fax: +44 (0)207 939 0981
Website: www.ecoconsulting.net

This email and any files transmitted with it are confidential and intended solely for the addressee. If you are not the named addressee you should not disseminate, distribute, copy, or alter this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100708/69dfc506/attachment.htm>


More information about the Equest-users mailing list