Does anyone know if the EER to EIR conversion mentioned below applies to
chiller COP values? For instance, if chiller data lists a full load
efficiency of COP 3.1/EER 10.5, do we then apply the EIR conversion and
enter that into the eQuest chiller EIR space?
 
Also, does anyone have a way of extrapolating a partial load curve for
any cooling equipment that lists a full load EER and an IPLV EER? The
equation for IPLV is:
IPLV = 0.01A 0.42B 0.45C 0.12D 
where
A = COP at 100% load and an ECWT of (85F)
B = COP at 75% load and an ECWT of (75F)
C = COP at 50% load and an ECWT of (65F)
D = COP at 25% load and an ECWT of (65F)
 
Unfortunately, I think I have too many variables and not enough data
 
 
 
Kathryn Kerns
Systems Specialist
BCE Engineers, Inc.
| Ph: 253.922.0446 | Fx: 253.922.0896 | 
 
 
 
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Supriya
Goel
Sent: Wednesday, January 13, 2010 5:13 PM
To: Katie Tuttle
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Cooling EIR and unit EER
 
Hello
 
I've attached the document. Though it is nothing more than a sheet out
of our assignment for the eQuest class.
I do not have the original document from where this would have been
taken. Hopefully this helps :)
 
Regards
Supriya
 
On Wed, Jan 13, 2010 at 4:28 PM, Katie Tuttle <Katie.Tuttle at hei-eng.com>
wrote:
I would be curious to see that document.  Would you mind posting it?
Thanks!
 
From: equest-users-bounces at lists.onebuilding.org [mailto:
equest-users-bounces at lists.onebuilding.org] On Behalf Of Supriya Goel
Sent: Wednesday, January 13, 2010 5:22 PM
To: Jacob Goodman
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Cooling EIR and unit EER
 
Jacob
 
You're right, EIR is not equal to 1/(EER/3.14)
 
The equation used by eQuest for calculating EIR from EER is-
 
COOLING-EIR = (1/EER - 0.012167) / ((1 / 3.413) + 0.012167)
 
If you want more information, I could send you the document from where I
got this.
 
Regards
Supriya
 
On Wed, Jan 13, 2010 at 4:11 PM, Jacob Goodman <jacobg at lseng.com> wrote:
How does eQuest calculate "cooling electrical input ratio" shown in
detailed edit mode when you input an EER in the wizard? >From a few
checks I've done cooling EIR doesn't equal 1/(EER/3.413) as I would
expect.
Jacob 
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to 
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-- 
Graduate Student, MSBE
School of Architecture and Landscape Architecture
Arizona State University, Tempe
This email and any files transmitted with it are confidential and
are intended solely for the use of the individual or entity to whom
they are addressed.  This communication represents the originator's
personal views and opinions, which do not necessarily reflect those of
Henderson Engineers, Inc.  If you are not the original recipient or the
person responsible for delivering the email to the intended recipient,
be advised that you have received this email in error, and that any use,
dissemination, forwarding, printing, or copying of this email is
strictly
prohibited.  If you received this email in error, please immediately
notify administrator at hei-eng.com.
 
 
 
 
 
-- 
Graduate Student, MSBE
School of Architecture and Landscape Architecture
Arizona State University, Tempe
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100126/cb701946/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Loads-Simulation Assignment House data part2 rev2.pdf
Type: application/pdf
Size: 432313 bytes
Desc: Loads-Simulation Assignment House data part2 rev2.pdf
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100126/cb701946/attachment.pdf>
-------------- next part --------------
An embedded and charset-unspecified text was scrubbed...
Name: ATT399459.txt
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100126/cb701946/attachment.txt>
    
    
More information about the Equest-users
mailing list