[Equest-users] Primary and Secondary Loop Problem
    Howe, Timothy 
    Timothy.Howe at stantec.com
       
    Fri Jan 22 11:45:28 PST 2010
    
    
  
 
Connect your coils to the secondary loop.  Right now they are not seeing
any load.
Timothy Howe, MS, LEED(r) AP
Mechanical Engineer
Stantec
2060 Brighton-Henrietta Town Line Road
Rochester NY 14623-2792
Ph:   (585) 413-5347
Fx:    (585) 272-1814
Cell: (585) 330-8681
www.stantec.com
The content of this email is the confidential property of Stantec and
should not be copied, modified, retransmitted, or used for any purpose
except with Stantec's written authorization. If you are not the intended
recipient, please delete all copies and notify us immediately.
Please consider the environment before printing this email.
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
omoltay at mimtarch.com
Sent: Friday, January 22, 2010 2:14 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Primary and Secondary Loop Problem
Dear All,
In my model, when I use only primary loops for chilled water and hot
water distribution, everything works OK. However, when I create
secondary loops to make the model more realistic to reflect distribution
system branching, I get an error message similar to the following on my
secondary chilled water loop and the simulation aborts (I suppose I
would get the same message for my other secondary loops if the
simulation were to continue):
"[Secondary] loop has zero design flow. Check input consistency."
Thanks for any help,
Omer Moltay, LEED AP
Mimta Ltd.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
    
    
More information about the Equest-users
mailing list