[Equest-users] Walls and Zones
    David C Stewart 
    david.c.stewart at state.or.us
       
    Tue Jan 12 09:11:29 PST 2010
    
    
  
How do you define (i.e. placement) the boundary between the open office
space and the perimeter zone?  David 
>>> Katie Tuttle <Katie.Tuttle at hei-eng.com> 1/12/2010 8:07 AM >>>
Based on some responses I’ve received regarding walls, spaces and
zones in eQuest, here’s my stab at summarizing what I’ve learned:
 
Walls
1.       Walls have 3 functions
a)      Transfer Heat
b)      Store Heat
c)       Reflect Daylight
2.       Interior wall types
a)      Standard interior
                                                         i.           
Transfers Heat
                                                       ii.           
Stores Heat
                                                      iii.           
Reflects Daylight
b)      Air Wall
                                                         i.           
Transfers heat
                                                       ii.           
Reflects Daylight
c)       Adiabatic
                                                         i.           
Stores Heat
                                                       ii.           
Reflects Daylight
d)      Internal Interior
                                                         i.           
Stores Heat
                                                       ii.           
Reflects Daylight
3.       For heat transfer to occur, you MUST have a wall.  Deleting
walls between spaces that are actually open air will cause eQuest to NOT
transfer any heat between these two spaces.  For example:
a)      Open office space with a perimeter and core zone.  
                                                         i.           
In order for heat transfer to occur between those two areas (as it
actually would) a wall must exist between them.  
                                                       ii.           
That “wall” would need to have a high u-value.  The surface
reflectance of that wall may need to be tweaked to simulate daylight
passing through it and reflecting back into that area since DOE-2 treats
air-walls as opaque (for all practical purposes).
                                                      iii.           
If the interior wall were just deleted between the perimeter zone and
core zone of the open office space, no heat transfer will occur during
simulation.  
                                                     iv.           
This lack of heat transfer could affect this zone, for example, when
it’s quite cold outside and that perimeter zone is losing heat –
without the benefit of some of the interior zone’s heat, that
perimeter zone would have to make up all of that heat loss (which
wouldn’t actually occur).
Spaces
1.       eQuest can only have one SPACE per ZONE.
2.       When creating your spaces in the wizard (or detailed mode),
make sure you zone this per thermostat, not per room.
 
Thanks for everyone’s responses!
 
KATIE L. M. TUTTLE EI, LEED® AP
Mechanical Designer
 
Henderson Engineers, Inc.   8325 Lenexa Drive  Lenexa, KS 66214
dir 913 742 5508  tel 913 742 5000  fax 913 742 5001   www.hei-eng.com
<http://www.hei-eng.com/> 
 
From: Sara Lewis [mailto:SLewis at tesengineering.com] 
Sent: Tuesday, January 12, 2010 7:55 AM
To: Katie Tuttle
Subject: RE: [Equest-users] Walls and Zones
 
I think (and could be wrong because I am VERY new to eQUEST) that you
could assign the different spaces to the same zone on the “zone group
definitions” tab of the building design wizard.  You’re able to name
your zone, pick the spaces that belong to that zone, and also specify
the HVAC system that serves that zone.  
 
Sara Lewis
 
tesengineering
providing dependable guidance since 1993
Sara Lewis
phone: (440) 614-0325
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Katie Tuttle
Sent: Tuesday, January 12, 2010 8:52 AM
To: James Hansen; omoltay at mimtarch.com;
equest-users at lists.onebuilding.org 
Subject: Re: [Equest-users] Walls and Zones
 
To follow up on the previous questions, I’ve wondered the same thing
– what if you want to assign multiple spaces to one zone in eQuest? 
For example, two rooms are being supplied by the same VAV box.  They
need to be created as two SPACES (on the “Building Shell” and
“Internal Loads” tabs) because of different internal loads, but
then on the “Air-Side HVAC” tab, both of the spaces need to be
assigned to one ZONE.  Is this possible?
 
Thanks!
 
KATIE L. M. TUTTLE EI, LEED® AP
Mechanical Designer
Henderson Engineers, Inc.   8325 Lenexa Drive  Lenexa, KS 66214
dir 913 742 5508  tel 913 742 5000  fax 913 742 5001   www.hei-eng.com
<http://www.hei-eng.com/> 
 
 
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
James Hansen
Sent: Tuesday, January 12, 2010 6:31 AM
To: omoltay at mimtarch.com; equest-users at lists.onebuilding.org 
Subject: Re: [Equest-users] Walls and Zones
 
Instead of deleting interior walls, why not just convert them do a
different type?  If I have a large open office with multiple zones, I'll
just set up all interior walls to be of type "Air".
 
Here are the available wall types from the help file:
 
INT-WALL-TYPE
Specifies the type of interior wall through code-words that identify
the type of heat transfer that occurs across the wall.
 
STANDARD                  
 
The default. Designates an interior wall that separates two spaces and
conducts heat between the spaces. It can be defined with a CONSTRUCTION
with TYPE=U-VALUE or TYPE=LAYERS although the heat storage effects of
the wall are accounted for only if TYPE=LAYERS. If you choose a
CONSTRUCTION with TYPE=U-VALUE, the U-value should be less than 0.709
Btu/ft2-F-hr (4.02 W/m2-K), which is the limiting value for two air
films and a very low resistance solid layer.  The NEXT-TO keyword is
required for this wall type. However, if the NEXT-TO space is the same
as the space in which the wall was defined, the program will change
INT-WALL-TYPE to ADIABATIC.
 
ADIABATIC                  
 
Designates an interior surface that does not conduct heat between
spaces but can store heat. This type should be used to separate spaces
that are considered to be identical and are, therefore, defined with
MULTIPLIER or FLOOR-MULTIPLIER in the SPACE command. An example is the
wall, ceiling, or floor that separates identical spaces that are
side-by-side on one floor of a building or above one another in a
multistory building. This type of wall should have delayed
construction.
 
INTERNAL                   
 
Designates an interior surface that lies completely inside a space. An
example is a water wall used to store solar energy in a space. Another
example is a wall between two rooms that are modeled as a single space.
This type of wall should have a construction with TYPE=LAYERS; in this
case the thermal mass of the wall will be considered in the space's
custom weighting factor calculation
 
AIR                             
 
Designates a non-physical interior surface with no mass (i.e., an
opening between spaces) across which convection can take place. This
type of wall should have a CONSTRUCTION with TYPE=U-VALUE. In this case,
we recommend an approximate U-value of 2.7 Btu/ft2-hr (15.3 W/m2). The
NEXT-TO keyword is required for this wall type.
 
                                  
If the "AIR wall" is part of a daylit space, its INSIDE-VIS-REFL values
need to be specified (even though it is not a physical wall) since
daylight can be reflected back across the AIR wall from the adjacent
space. The values to use for INSIDE-VIS-REFL in this case are determined
as follows. Assume that the AIR wall, of area A, is defined in space 1
and separates space 1 and space 2. Let the spaces have inside surface
area Si (excluding the AIR wall) and area-weighted visible reflectance
ri excluding the AIR wall). Then INSIDE-VIS-REFL=(R2 , R1) where Ri is
the cavity reflectance of space i given by
            Ri = A * ri / (Si - (Si -A)*rI)
 
 
 
 
GHT Limited
James Hansen, PE, LEED AP
Senior Associate
1010 N. Glebe Rd, Suite 200
Arlington, VA  22201-4749
703-338-5754 (Cell)
703-243-1200 (Office)
703-276-1376 (Fax)
www.ghtltd.com 
 
 
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
omoltay at mimtarch.com 
Sent: Monday, January 11, 2010 6:54 PM
To: equest-users at lists.onebuilding.org 
Subject: [Equest-users] Walls and Zones
 
Dear all,
 
I have not received a reply to my previous question, so here is a
simplified version of it: I see that everytime I create a zone in the
Wizards, eQuest builds walls around these zones. Does every zone (or
every
space) need to have walls around? Would it be a problem if I delete
these
walls afterwards?
 
For example, when I have a large open office, I would like to have
several
zones. So after the Wizard creates the building description, I have to
delete all the walls around these zones.
 
Is this normal procedure?
 
Thanks,
 
Omer Moltay, LEED AP
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
 
The information contained in this communication is confidential, may be
privileged, and is intended only for the use of the addressee.  It is
the property of GHT Limited.  Unauthorized use, disclosure or copying of
this communication or any part thereof is strictly prohibited and may be
unlawful.  If you have received this communication in error, please
notify me immediately by return e-mail or by e-mail to ght at ghtltd.com,
and destroy this communication and all copies thereof, including all
attachments.  Thank you.
 
 
 
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG 
 
This email and any files transmitted with it are confidential and
are intended solely for the use of the individual or entity to whom
they are addressed.  This communication represents the originator's
personal views and opinions, which do not necessarily reflect those of
Henderson Engineers, Inc.  If you are not the original recipient or
the
person responsible for delivering the email to the intended recipient,
be advised that you have received this email in error, and that any
use,
dissemination, forwarding, printing, or copying of this email is
strictly
prohibited.  If you received this email in error, please immediately
notify administrator at hei-eng.com.
 
 
 
 
 
    
    
More information about the Equest-users
mailing list