[Equest-users] Heating Energy in ASHRAE 90.1 Appx G Baseline System 4
Kendra Tupper
ktupper at rmi.org
Wed Feb 24 10:56:59 PST 2010
Lawrin,
In the baseline model, you have zero outside air which is why the heating
energy is so low. You have specified that you're pulling OA from another
system, which appears to be an artifact from setting up a DOAS for the
Proposed model perhaps? Restore default on that input.
Also, when I ran the models in eQUEST the Proposed used 634,370 kWh/yr and
the Baseline used 690,870 kWh/yr, so I'm not sure where the 1/63rd of the
energy use was coming from.
Kendra Tupper, PE, LEED AP
Senior Consultant
Built Environment Team
Rocky Mountain Institute | T 303-567-8641 | F 303-245-7213 |
www.rmi.org
On Wed, Feb 24, 2010 at 2:27 AM, Ellis, Lawrin <lawrin.ellis at tlc-eng.com>wrote:
> Good morning All.
>
>
>
> We are modeling a two-story college classroom building in Fort Myers,
> Florida. Per ASHRAE 90.1-2004 App'x G, Table G3.1.1A, the baseline building
> is modeled using System 4, PSZ-HP. The proposed design is chilled water VAV
> with electric strip heat. We have completed numerous models comparing these
> system types previously using VisualDOE with results, as expected, showing
> the baseline building consuming approximately 1/3 (or slightly less) of the
> energy used by the proposed design. However, as modeled in eQUEST, when
> comparing the baseline building heating energy to the proposed design,
> results show the baseline building using approximately 1/63rd of the heating
> energy used by the proposed design. Internal loads are almost identical in
> both the proposed and baseline models. The outdoor air flow and humidity
> controls are identical in each model. Also, comparing peak design
> conditions in the simulation output shows the baseline building losing heat
> at approximately twice the rate of the proposed design. We are at a loss
> trying to determine why the heating energy is virtually non-existent in the
> baseline model.
>
>
>
> Models are attached for reference. Any insight or assistance is greatly
> appreciated. Thanks in advance and kind regards,
>
> *Lawrin T. Ellis, PE *
>
> LEED AP, CxA
>
> *Associate, Mechanical Project Engineer*
>
>
>
> *TLC Engineering for Architecture
> **Your Architecture 2030 Partner*
>
>
>
> 1400 Colonial Boulevard, Suite 203
>
> Ft. Myers, FL 33907
>
>
>
> phone:
>
> 239-275-4240
>
> fax:
>
> 239-275-3511
>
> cell:
>
> 239-292-3776
>
> website:
>
> www.tlc-engineers.com
>
>
>
> [image: http://www.tlc-engineers.com/images/TLC_Sig_Loc_Block.gif]<http://www.tlc-engineers.com/>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100224/406c4eee/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/gif
Size: 5272 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100224/406c4eee/attachment.gif>
More information about the Equest-users
mailing list