[Equest-users] Outside airflow (eQuest Users group)

Dakota Kelley dakotak at teliospc.com
Wed Feb 24 10:37:06 PST 2010


I agree with Karen.  Appendix G is pretty clear that ventilation rates should be identical in both cases unless the proposed case is using DCV, and there is an implied understanding that the proposed OA rates meet code, whether that be 62.1 or the applicable local code.  Some people make the mistake of using the same percentage of outside air in both cases, but it’s the flow rates that need to be identical, not the percentage.  I find that this usually requires entering a CFM at the zone level, particularly for multi-zone systems, and the elevation factor needs to be applied if the project is not at sea level (that is, if you want output reports to match the design documents exactly).

 

With respect to the review comment, I would just hold your ground and follow your (correct) interpretation of Appendix G.  I’ve had conflicting review comments on previous projects, too.  Sometimes the reviewer is simply misinformed.

 

                                

                         DAKOTA KELLEY                                                              

                                Project Designer

 

                                Office:      214-744-6199

                                Cell:         214-280-3825

                                Fax:         214-744-0770 

                

http://www.teliospc.com <http://www.teliospc.com/>           3535 Travis St. Suite 115 

dakotak at teliospc.com <mailto:dakotak at teliospc.com>              Dallas, TX 75204 

 

| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |                         

 

 

CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed, 

And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you 

are not the intended recipient, please email the sender immediately, and delete this email from all computers.  Any 

distribution or other use is strictly prohibited.  Copyright © 2010 Telios Corporation.

 

 

 

 

From: Karen Walkerman [mailto:kwalkerman at gmail.com] 
Sent: Wednesday, February 24, 2010 8:57 AM
To: Tomlinson, Scott
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Outside airflow (eQuest Users group)

 

I have always sized the outdoor air to be the same in the proposed and baseline buildings.  There is a section in Appendix G that specifically directs the modeler to do this.  I have had a number of buildings approved using this method.

--
Karen

On Wed, Feb 24, 2010 at 9:06 AM, Tomlinson, Scott <stomlinson at smma.com> wrote:

Thank you to those who helped with my previous outside air question.  I now understand how the outside air is controlled, I’m just not sure how I should be setting it.  ASHRAE 90.1 – 2004 dictates that the minimum outdoor air ventilation rates should be the same for the design and baseline building, but one of our LEED review comments is that our baseline model should be modeled base on ASHRAE 62.1 – 2004 requirements.  It seems that if I let eQuest size my OA based on ASHRAE 62.1 I won’t match my design building OA rates (in this case, 100%).  Also, if I let eQuest size my OA based on the 100% OA rate of my design building I will be over ASHRAE 62.1 requirements. 

What method of outside air sizing have y’all been using for your models, and have you been approved by USGBC with the method?

 

-          Thank you,

 

__________________________________________

Scott Tomlinson, PE, LEED-AP

Mechanical

Symmes Maini & McKee Associates, Inc.

1000 Massachusetts Avenue, Cambridge, MA 02138

t: 617.520.9438

Error! Filename not specified.

 

f: 617.354.5758

stomlinson at smma.com

www.smma.com <http://www.smma.com/> 

 

 


_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG





-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100224/7dab72d8/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 3170 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100224/7dab72d8/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100224/7dab72d8/attachment.jpeg>


More information about the Equest-users mailing list