I will partially/fully address your questions - be advised you will need
to provide more specific info to get more specific answers however:
1. Are you trying to define your constructions within the wizard mode?
If so, you can easily define a 6" concrete wall with wood-furred
insulation there to match your desired construction. It's done in one
of the first wizard screens for each of your shells.
2. I'm struggling to understand why you would want to create shells
within shells. Though there may be a significant volume of space above
the interior "rooms," I would simply define them as separate zones with
a huge plenum "zone." If accuracy is paramount and you suspect there
might be a huge accuracy hit by defining those spaces above the
low-ceiling rooms to be separate spaces, you can later in detailed mode
ensure the "plenums" above these rooms are thermally tied to the
remainder of the open warehouse zone surrounding them.
I'd suggest two shells only based on what you're describing: One for
main building and one for warehouse.
Regarding getting started and wishing for training, let me suggest
bookmarking these two archive searching pages:
a. http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/
b.
http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/
...and then reading this email I wrote regarding "beginner's advice" for
some very general pointers:
c.
http://lists.onebuilding.org/htdig.cgi/equest-users-onebuilding.org/2009
-November/002534.html
Best of luck!
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Curtis
Strobehn
Sent: Thursday, February 18, 2010 1:43 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Message
to all Equest users.
I'm still learning Equest.
had a few questions.
1. I'm creating a main buildind that is connected to a warehouse. I'm
creating main building with a 6" concrete wall, and there is a frame
builting side the outside concrete wall.
How do it create the model? outside shell with concrete, the
inside shell
create wood frame.
Or is there away to build one shell and build it up by adding
the Batt
Insulation? not sure.
2. The Warehouse is joining build to main building. within the warehouse
there is an alcove and two smaller buildings within the warehouse.
There is a sprinkler riser room and IT room and a storage room
that is only
9' high floor to ceiling and floor to floor 14'.
This is all within the warehouse.
From what I understand so far with Equest. I will have to create
sprate
shell for each room. warehouse 1 shell, Sprinkler room sparet shell, IT
Room Sparate shell, Alcover sparate shell uncondution, and storage room
sprate shell.
Is this correct to create sprate shell to build a model?
Wish had training DVD or something.
can anyone help?
Curt.strobehn at eesinet.com
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
More information about the Equest-users
mailing list