[Equest-users] Above Roof Canopy Modeling

Nick Caton ncaton at smithboucher.com
Thu Feb 18 12:50:10 PST 2010


Happy to help Reniel =),

 

I suppose I introduced a number of general points regarding building shade effects that will not all apply to your specific project, so apologies if this wasn’t clear – just trying to feed some ideas to consider.

 

I think I understand your results and will restate/summarize them to ensure we’re on the same page: 

1.       Fully opaque (0% transmittance) results in lower energy figures

2.       Fully translucent (100% transmittance) results in higher energy figures

3.       Heating varies more than cooling.

4.       What you find to be weird/unintuitive in your results is that space heating energy rises with transmittance.  Put another way (more clear to my thinking): heating energy spent lowers when you introduce a building shade.

 

To emphasis one of my suggestions:  Do you have daylighting dimming/switching controls?  Less daylight resulting in un-dimmed light fixtures means more heat incident from the fixtures, and simultaneously less energy spent for the space heating figure as the lights become a more significant local heat source.

 

Kim’s suggestion regarding retained radiative heat is another possibility – While I can’t personally speak to whether that’s actually in play in eQuest between building shades and the rest of the model, I’d definitely like to know if somebody is sure of it!

 

While shades as a general practice will cause energy to rise in cooling months (by blocking solar gains incident on walls/windows), if you have low winter sun angles and the courtyard facades in question aren’t getting much incident sunshine in the first place (being blocked by other parts of the building), then it would be normal for the shades’ expected negative winter effects to lower or be non-existent.  In such a situation, otherwise smaller effects including retained radiative heat or lighting space heating as mentioned above could cause the energy figures to swing in an unexpected direction.

 

Again, I can’t offer any specific answers, but hopefully this offers a bit of guidance that will help you investigate the problem.  I’d still encourage you to determine which specific space heating/cooling load components are changing – they may provide a specific clue as to whether these results are to be expected or an indication something isn’t being modeled correctly.

 

Best of luck!


~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: Shinn, Kim [mailto:kim.shinn at tlc-eng.com] 
Sent: Thursday, February 18, 2010 12:41 PM
To: reniel barroso; Nick Caton; Dakota Kelley; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Above Roof Canopy Modeling

 

Reniel:

 

Believe it or not, but I think that the program allows for night-time radiative cooling.  So, on a cold winter night, without the canopy, the building cools to the black-body of space.  With the canopy, that radiative cooling path is blocked and the building retains heat.

 

Kim E Shinn, PE, LEED AP BD+C, CxA

Senior Sustainability Consultant

 

From: reniel barroso [mailto:renielbarroso at yahoo.com] 
Sent: Thursday, February 18, 2010 12:08 PM
To: Shinn, Kim; Nick Caton; Dakota Kelley; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Above Roof Canopy Modeling

 

Thanks.
I appreciate each of your insights.

The project is in Middle East so everybody can have a clearer picture of the error in numbers.

I'll check Kim's point on low solar altitudes.

I just couldn't relate Nick's point on the numbers that I have.
Please take note that the more transmittance I introduced in the courtyard, the more space heating it requires on spaces facing the courtyard and vice versa.
Is it correct?
I couldn't relate it to cooling-heating fundamentals.
Nick, please confirm your point by clarifying these issues.

Thank you so much.


Reniel

 

 

________________________________

From: "Shinn, Kim" <kim.shinn at tlc-eng.com>
To: Nick Caton <ncaton at smithboucher.com>; reniel barroso <renielbarroso at yahoo.com>; Dakota Kelley <dakotak at teliospc.com>; "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Thursday, February 18, 2010 19:55:43
Subject: RE: [Equest-users] Above Roof Canopy Modeling

Another possible issue on the cooling side:  In some climates, and in some building configurations, we see very high cooling loads in the fall, winter and spring (e.g, The Middle East).  Ambient temperatures moderate somewhat from summer extremes, but the low solar altitudes are throwing radiation load at the windows at a much more direct angle, frequently “under” the lip of our overhangs and canopies.

 

Kim E Shinn, PE, LEED AP BD+C, CxA

Senior Sustainability Consultant

 

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Thursday, February 18, 2010 9:29 AM
To: reniel barroso; Shinn, Kim; Dakota Kelley; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Above Roof Canopy Modeling

 

Without more specifics, I think we can only give you some general advice/suggestions…  I haven’t tried this, but if you’re trying to observe results with/without the shade, maybe you should just delete the shade instead of altering transmittance and see if anything changes?

 

Overhangs/shades/canopies and the like can both help and hurt over the course of the year.  From what we’ve heard I don’t think you’re doing anything wrong in application.  I might take these results as a sign you need to carefully reconsider your canopy design with respect to how it is blocking sunlight.

 

Rather than focusing on overall cooling/heating energy spent, you might do well to identify which specific internal/external load components are changing significantly.  If you have any daylighting controls specifically, watch carefully what’s happening to your lighting energy spent.

 

The increase in heating energy is likely because you’ve eliminated a significant amount of solar gains through fenestrations and opaque walls by blocking the sun during heating months.  Remember that building shades are shading more than windows!

 

In the heating months and from an energy-perspective, a perfect window shade blocks only as much direct sunlight as is required to prevent glare issues through windows.  Any other direct light is welcome as a free heating source – both on windows and opaque walls.  

 

The lesser increase in cooling energy probably has a less direct conglomeration of reasons…  That it’s relatively minor suggests it could be a lot of things.  I would look at whether your simultaneous cooling/heating hours are changing.  For review:  In cooling months, a perfect shade blocks (reflects away) direct light incident on windows and opaque walls to minimize solar thermal loads, but still lets indirect light inside windows for daylighting purposes without obstructing views to an unacceptable level.  

 

Another potentially odd daylight/thermal behavior interaction I’ve observed:  If you end up really cutting down your lighting energy spent, you might observe a corresponding increase in heating energy spent, as you’re effectively eliminating a heating source in the winter by not running your lights at 100%.

 

~Nick



 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: reniel barroso [mailto:renielbarroso at yahoo.com] 
Sent: Thursday, February 18, 2010 6:27 AM
To: Shinn, Kim; Nick Caton; Dakota Kelley; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Above Roof Canopy Modeling

 

Hi!

 

Thanks for your replies.

It helps us a lot.

 

On the model that we're working on,

We already did what everyone suggested.

We modeled the canopy as fixed shading.

 

To double check if the model is running as what we're expecting based on cooling load fundamentals,

We modeled full opaque canopy (0 transmittance) and 1.0 transmittance for comparison purposes only.

 

After running the model, we had weird results:

 

0 transmittance

Chilled Water - 104.05 MBTU

Space Heating - 74.8 kwh (X000)

 

1.0 transmittance

Chilled Water - 109.9 MBTU

Space Heating - 96.2 kwh (X000)

 

Am I modeling it wrong?

Am I missing something?

Are we having the same results especially with the heating consumption?

What are the areas that I should check first before concluding?

Note that we modeled the systems for both as AUTOSIZING.

 

Thanks for your assistance.

 

 

Reniel


 

 

________________________________

From: "Shinn, Kim" <kim.shinn at tlc-eng.com>
To: Nick Caton <ncaton at smithboucher.com>; Dakota Kelley <dakotak at teliospc.com>; reniel barroso <renielbarroso at yahoo.com>; "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
Sent: Wednesday, February 17, 2010 21:44:23
Subject: RE: [Equest-users] Above Roof Canopy Modeling

At the risk of piling on more information than you really wanted:

 

App G allows you to take advantage of shading – so, remove shading from your 90.1 baseline.

 

You can assign schedules, transparency and reflectance to shades.  If you want to model the effect of deciduous trees planted near the building, for instance, you can use a schedule to have greater transparency in the winter (for passive solar heating) and less transparency in the summer for shading.

 

Kim E Shinn, PE, LEED AP BD+C, CxA

Senior Sustainability Consultant

 

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Wednesday, February 17, 2010 11:29 AM
To: Dakota Kelley; Shinn, Kim; reniel barroso; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Above Roof Canopy Modeling

 

Thanks Dakota!

 

This is good to know as I have a situation where it would probably be less work to explore some specific overhang/fin options within my complex eQuest model vs. trying to build a separate model through my more usual daylight analysis workflows.

 

Bonus points for your response being 10x more clear than my question =)!

 

~Nick

 



 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: Dakota Kelley [mailto:dakotak at teliospc.com] 
Sent: Wednesday, February 17, 2010 11:16 AM
To: Nick Caton; Shinn, Kim; reniel barroso; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Above Roof Canopy Modeling

 

Window shades only shade their parent window, not the walls.  Building shades will shade everything in their shadow, and they rotate with the building if the azimuth is changed.  Fixed shades also shade everything in their shadow, but they do not rotate with the building.

 

                                

                         DAKOTA KELLEY                                                              

                                Project Designer

 

                                Office:      214-744-6199

                                Cell:         214-280-3825

                                Fax:         214-744-0770 

                

http://www.teliospc.com <http://www.teliospc.com/>           3535 Travis St. Suite 115 

dakotak at teliospc.com <mailto:dakotak at teliospc.com>              Dallas, TX 75204 

 

| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |                         

 

 

CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed, 

And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you 

are not the intended recipient, please email the sender immediately, and delete this email from all computers.  Any 

distribution or other use is strictly prohibited.  Copyright © 2010 Telios Corporation.

 

 

 

 

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Wednesday, February 17, 2010 11:10 AM
To: Shinn, Kim; reniel barroso; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Above Roof Canopy Modeling

 

Here is another illustration shading a courtyard of sorts.  You’re looking at the dark grey rectangle in both examples.

 

I have a followup actually for others familiar with creating building shades – are they any different in behavior from a window shade, or are they the same thing simply defined in different ways?  More specifically, do window shades shade buildings and can I define building shades as a means of modeling multiple vertical fins/horizontal light shades per window?  

 

 

 

~Nick



 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Shinn, Kim
Sent: Wednesday, February 17, 2010 9:03 AM
To: reniel barroso; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Above Roof Canopy Modeling

 

Reniel:

 

What you need is an exterior shade.

 

In detailed edit mode, go to Building Shell and select Fixed Shades (or a Building Shade, depending on whether you want the shade to be attached to the building – as it rotates, for instance).  A fixed shade remains fixed in space.  This is a good way to model adjacent buildings.

 

 

 

Right click on Fixed Shade and go through the dialog boxes.

 

Kim E Shinn, PE, LEED AP BD+C, CxA

Senior Sustainability Consultant

 

From: reniel barroso [mailto:renielbarroso at yahoo.com] 
Sent: Wednesday, February 17, 2010 8:22 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Above Roof Canopy Modeling

 

Hi to All,

 

We are modeling 3 buildings interconnected with each other.

A large canopy is covering the roof of the buildings and partially shading the courtyard within these buildings.

 

Can we model this canopy in eQuest? How?

Can we model its effect on the cooling load of spaces facing the courtyard?

We are expecting that solar heat gain will be lower on fenestrations of the rooms/spaces facing courtyard due to shading compared to perimeter spaces facing outside the development.

 

Thanks in advance.

 

 

Reniel

 

 

 

 

________________________________

New Email addresses available on Yahoo! <http://sg.rd.yahoo.com/aa/mail/domainchoice/mail/signature/*http:/mail.promotions.yahoo.com/newdomains/aa/> 
Get the Email name you've always wanted on the new @ymail and @rocketmail.
Hurry before someone else d

 

________________________________

Get your preferred Email name! <http://sg.rd.yahoo.com/aa/mail/domainchoice/mail/signature/*http:/mail.promotions.yahoo.com/newdomains/aa/> 
Now you can @ymail.com and @rocketmail.com.

 

________________________________

Get your preferred Email name! <http://sg.rd.yahoo.com/aa/mail/domainchoice/mail/signature/*http:/mail.promotions.yahoo.com/newdomains/aa/> 
Now you can @ymail.com and @rocketmail.com.

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100218/ab798f25/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100218/ab798f25/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 2327 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100218/ab798f25/attachment-0001.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 529962 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100218/ab798f25/attachment.png>