[Equest-users] WLHP & Lack of an ERV
Demba Ndiaye
Demba.Ndiaye at setty.com
Tue Feb 16 13:47:46 PST 2010
Dennis,
Extract from eQuest Help;
"A water loop heat pump can also be modeled using a PVVT, PSZ or PVAVS system be selecting a HEAT-SOURCE as HEAT-PUMP combined with specifying that the CONDENSER-TYPE is WATER-COOLED. This alternate method of building a WLHP model allows the use of the many options that are available for those types of systems; many of those options are not available for the HP type of system."
So take a PSZ, a PVVT or a PVAVS depending on what you have. In doing so, these components act like a HP. This is one way to model what you want.
____________
Demba NDIAYE
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of O'Connor, Dennis CAR
Sent: Tuesday, February 16, 2010 4:43 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] WLHP & Lack of an ERV
Fellow Equest-Users,
I would greatly appreciate it, if someone would take a moment to explain the following:
Why doesn't eQUEST allow airside heat recovery with water loop heat pumps? HAP does allow this type of application.
I went through the archives and was unable to find an answer to my question.
Does anyone know of a work around using a WLHP?
Thanks in advance for taking the time to review my question,
Dennis O'Connor
Graduate Student at the University of Hartford
[cid:image001.jpg at 01CAAF27.6DA362D0]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100216/cf78c49a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 13120 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100216/cf78c49a/attachment.jpg>
More information about the Equest-users
mailing list