[Equest-users] DHW Loads - What is the Process Flow in gpm?
Sundharam, Premnath
psundharam at DLRGROUP.com
Mon Feb 15 15:44:15 PST 2010
Hey Mike,
Thanks for the response. I did have the inlet temp. that I used in my
hand calcs as a schedule (because the inlet temp. changes) and what is
interesting is... I was running Savings by Design compliance and the
savings by Design run was predicting the higher MBTUs. Just out of
curiosity I tried running just a simulation under eQuest with all the
below mentioned values and eQuest simulation predicted 2,359 MBTUs -
closer to our hand calc. So I am not sure how and why Savings by Design
is different.
So is my understanding of the Process Flow as expected daily gpm
correct?
For solar, is it just a subtraction of energy usage as a post - savings
by design measure or is there a better way to model it in eQuest?
Thanks.
Prem
From: Michael Andelman [mailto:mike at andelmanlelek.com]
Sent: Monday, February 15, 2010 3:39 PM
To: Sundharam, Premnath
Subject: RE: [Equest-users] DHW Loads - What is the Process Flow in gpm?
Try entering the inlet temperature you used in your calcs instead of
defaulting to the ground temperature.
Mike Andelman
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Sundharam, Premnath
Sent: Monday, February 15, 2010 4:52 PM
To: equest-users at lists.onebuilding.org
Cc: Wohlgenant, Terry
Subject: [Equest-users] DHW Loads - What is the Process Flow in gpm?
Folks,
I am trying to understand modeling the DHW system in eQuest. I searched
through the list archives for posts. I found some information but still
am not clear.
Our project has the following:
1. 3 heaters per DHW loop and 1 DHW loop per building for FOUR
buildings.
2. Total occupants = 1526 and shower load is the major load
(lavatories are negligible)
3. We use a 1.2 gpm shower head.
4. We estimate a 12 min shower per day per occupant as the load
and the load does not vary through the year.
5. Hot water supply temperature is 105 F
6. Our storage gas water heaters are 92% efficient.
7. Our potable water comes from a reservoir and so I built a DHW
inlet water temperature schedule that reflects the changes per month
We also have a solar thermal system that using RETSCREEN we figured out
that it saves about 60% of the total hot water consumption.
Modeling attempt 1:
1. I used one single loop and one heater for the entire campus.
2. On the below screen shot for the DHW loop what is the Process
Flow in gpm?
a. Do I calculate it as below?
i.
Process flow = (1526 occupants x 1.2 gpm x 12 min per day) / (24 hours x
60 mins) = 15.26 gpm
ii.
And then assign a DHW_schedule that has 1.0 as the multiplier for all
the hours in the year
b. Or do I calculate it as below?
i.
Process flow = 1526 occupants x 1.2 gpm x 12 min per day / 60 mins per
hour = 366.24 gpm
ii.
And then assign a DHW_schedule that has basically "0" as the multiplier
for all the hours except "0.5" for 6 am to 7 am and "0.5" for 5 pm to 6
pm - this way I am allowing half of the occupants to take shower in the
morning and the other half in the evening and the rest of the hours
there is no demand - this close to reality!
c. Or do I count all the shower heads I have and figure out the
total gpm of the heads?
Screenshots of the inputs on the Loop:
Problems:
If I input the process flow as 15.26 gpm, eQuest is calculating the
total DHW energy consumption as 5,315 Million BTU but our hand calcs
only shows 2,298 Million BTUs.
So if any of you have any suggestions on getting the DHW load correct, I
would really appreciate that.
Also on the Solar Side, what is the best way to simulate this?
Again many thanks.
Prem
Premnath Sundharam, Assoc. AIA, LEED AP
Architectural Designer | Senior Associate
psundharam at dlrgroup.com
DLR Group
Architecture Engineering Planning Interiors
o: 602/381-8580
6225 North 24th Street, Suite 250 Phoenix, AZ 85016-2020
dlrgroup.com <http://www.dlrgroup.com/> | listen.DESIGN.deliver
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100215/3c6595fd/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 19523 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100215/3c6595fd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/png
Size: 20137 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100215/3c6595fd/attachment-0001.png>
More information about the Equest-users
mailing list