[Equest-users] Reproducing Unmet Hours

Demba Ndiaye Demba.Ndiaye at setty.com
Mon Feb 15 12:42:33 PST 2010


By dead band, do you mean the throttling range that eQuest defines? If so, there is a limit on how much you can increase it, due to the 5F minimum dead band requirements of the 90.1.

Demba.

From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach
Sent: Sunday, February 14, 2010 12:57 AM
To: STEVE SAMENSKI; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Reproducing Unmet Hours

Steve:

The NO. 1 thing I have found effective is to increase the deanband in the thermostat. I don't thin USGBC has any problem with that.

It also depends on wheather it is COOLING or HEATING unmet housers. Sometimes, you haven't provided a reheat vaule.

Try those first.

________________________________
From: STEVE SAMENSKI <steve at thespinnakergroupinc.com>
To: equest-users at lists.onebuilding.org
Sent: Sat, February 13, 2010 2:59:00 PM
Subject: [Equest-users] Reproducing Unmet Hours

It seems I spend a great deal of time with eQuest trying to reduce unmet hours in a model.  One thing I’ve tried is having eQuest produce an hourly report of a problem zone’s temperature and T-stat setting, exporting the data to Excel and then searching it for patterns.  This approach has a few problems:

 1.  I can barely figure out how to create the hourly report I’m looking for.  The reporting function (in the Detailed Data Edit mode, under Project & Site, Hourly Reports) isn’t very intuitive, and I can’t find any documentation on it.  Has anyone found the docs on this?  (I’m currently working through the relevant sections of the DOE 2-2 Dictionary, trying to cross reference between the inputs to eQuest and the BDL file generated from those inputs.  I’m just wondering if there’s a short-cut somewhere.)
 2.  Once I get the data in Excel and do some filtering, I can never get the exported data to match the unmet hours found in report SS-R.  The Excel analysis seems to always overstate the unmet hours.  Has anyone had any luck reproducing the SS-R values?  Any ideas?
 3.  I’d like to hear other user’s experience.  Do you find that resolving unmet hours is a significant part of your modeling time?

Steve Samenski, PE, LEED AP