[Equest-users] Stairwell
Bishop, Bill
wbishop at pathfinder-ea.com
Thu Feb 11 05:55:56 PST 2010
Rob,
I usually model staircases as one space/zone per floor. Doing this, you
have (at least) two options for modeling the fan coils. 1.) You could
enter them as designed on the first and third floors, and turn the floor
surfaces on the second and third floors to "air" construction. 2.) You
can put fan coils on all three floors and divide the total capacity by
three. I think option 1.) is more realistic but may result in unmet
heating hours on the second floor. Option 2.) is a little quicker but I
wonder how accurate the fan energy will be if you don't prorate the
static pressure. I also reduce my DESIGN-HEAT-T in stairwells and
mechanical spaces, and apply a different thermostat schedule with a
lower heating setpoint.
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Rob
Hudson
Sent: Thursday, February 11, 2010 8:34 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Stairwell
I would like to here people's opinion on the best approach to a
particular situation.
I have a model where the staircase is open and three stories tall, but
there is two fan coil units, on the first and third floors. Is it
better to model this as two spaces or as three spaces?
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20100211/60c4a24c/attachment.htm>
More information about the Equest-users
mailing list