1.  detailed mode, not wizard mode.
1b.  how many zones do you have?  equest/doe2.2 only recognizes up to 25 
meters.  i'm not sure if that's 25 electric and fuel combined or 25 
electric and 25 gas but i think it's the total number of meters.  i know 
from experience if you exceed 25 electric meters heating and cooling 
energy will not be reported properly and you'll have at least several 
thousand unmet load hours in cooling mode.

2.  are you looking to where you can add the calculated results to add 
together, or where to manually input the kw and fcu data?  for input 
data equest/doe2.2 only lets you assign one hvac unit per thermal zone 
so if you have multiple units serving a large area and you want to 
simulate the actual number of fc units you have to break that large area 
into smaller thermal zones - one for each fc unit.  in wizard mode this 
is really best done prior to adding custom windows - changing the zones 
erases all custom window data.
2.b  note, even in detailed mode, if you want to assign a cooling only 
unit to a zone and then choose a heating source (radiant slab) that is 
not an option for the cooling unit type equest won't let you do that for 
an existing zone.  if a zone is already assigned to a unit, i.e. 
evaporative cooler, and you want to add the same zone to a heating only 
system, i.e. radiant slab heat, an error message pops up that there are 
no available zones to assign to the system.

On 2/10/10 3:56 AM, Hind Dirani wrote:
> Dear All,
>
> I have two questions:
>
>   - How to model separate electric meters for each zone on eQuest.
>
>   - And where I can add the kW and numbers of FCU for each zone.
>
> Any suggestion would be appreciated, thanks.
>
> Hind
>